I have a customer that is trying to connect to the P116 relay but the usb driver is not installing. The customer has Easergy Studio 9.2. Where is the driver located so I can try to manually install the driver?
Link copied. Please paste this link to share this article on your social media post.
Dear @mike_zellhofer_
Good to know that the issue was solve.
We are here to help you in case you need.
BR
FLORIDA
Link copied. Please paste this link to share this article on your social media post.
Dear @mike_zellhofer_
I am in charge of Easergy Studio in the global marketing team.
Are you using any USB adaptor?
Link copied. Please paste this link to share this article on your social media post.
Dear @SergioFLORIDA
That is what I thought. I just wanted to be 100% sure. The customer was finally able to get it working with his IT group.
I just wanted to verify that Easergy Studio didn't have a USB driver for P116 relays hidden somewhere. It was just a direct usb connection form his laptop (Windows 7) to the P116.
The fix was to uninstall Easergy Studio completely and re-install. Then the driver was installed for the customer.
Thanks,
Mike
Link copied. Please paste this link to share this article on your social media post.
Dear @mike_zellhofer_
Good to know that the issue was solve.
We are here to help you in case you need.
BR
FLORIDA
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.