Hai !
May I know can we change the IEC 61850 Edition of the Micom C264 IED at site using HMI/any software? If so, Please share the procedure for changing .
Thanking you !
Link copied. Please paste this link to share this article on your social media post.
Hello Bhaskar,
Below steps may helps to downgrade the C264 relay
Use MiCOM S1 Studio or MiCOM C264 Configuration Tool:
Export the Current Configuration:
Prepare Edition 1-Compatible CID/ICD Files:
Load the Edition 1 Configuration:
Reboot and Test:
Validation: