Ask our Experts
Didn't find what you are looking for? Ask our experts!
New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.
Search in
Please select a country to continue with beta search.
Link copied. Please paste this link to share this article on your social media post.
Dear Sir/Madam !
I have one Schneider Micom P442 IED that equipped with IEC61850 Ed.2. This edition is not compaitable with my gateway. Can I change the IEC61850 Ed.2 to Edition 1 at site?
Link copied. Please paste this link to share this article on your social media post.
Hello @S_Bhaskar
Yes, you can switch from Edition 2 to Edition 1.
The switching can be done at the relay HMI. You will get the option to select the edition in "System Data" menu.
You have to create 61850 MCL file and write to the relay.
Link copied. Please paste this link to share this article on your social media post.
Hello @S_Bhaskar
Yes, you can switch from Edition 2 to Edition 1.
The switching can be done at the relay HMI. You will get the option to select the edition in "System Data" menu.
You have to create 61850 MCL file and write to the relay.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.