Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
2023-08-3112:01 PM
C434 Synchrocheck function
Hello all!
I´m working on a C434 application where it´s necessary to test a ANSI 25 function. In this particular application (breaker and a half topology) I don´t have the "Vref" voltage input available, so I´m activating the Meas V. (T9x) USER option in order to use the neutral voltage displacement input to synchronize with the three-phase voltage. It works perfectly for voltage synchronism, but it ignores the angle difference (It allows a close command with angle difference). Do you guys know what may be possibly happening? Below I took a screenshot of the configuration (including the setting for voltage and sync enable):