ANSI 87BB (High impedance busbar differential) in Powerlogic P5F30

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • ANSI 87BB (High impedance busbar differential) in Powerlogic P5F30
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Lt. Commander Araceli_Monje Lt. Commander
23
HenriGRASSET
Captain HenriGRASSET Captain
15
Rudolf_Simon
Commander Rudolf_Simon Commander
13
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Protection & Control
Solved
sungur
Crewman sungur Crewman
Crewman

Posted: ‎2025-02-11 12:49 AM

0 Likes
1
615
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-11 12:49 AM

ANSI 87BB (High impedance busbar differential) in Powerlogic P5F30

Hello everyone,

In the manual section of Powerlogi P5F30 series relays, it appears that ANSI 87 BB (High impedance busbar differential) protection can be done.

Required conditions;
11. Only available with conventional (phase or neutral) CTs.
12. Function can be realized by application guidelines.

However, when the appropriate relay is selected, ANSI87 protection does not appear under the Protecton tab in the E-setup easergy Pro software.

How do we do 87BB (High impedance busbar differential) protection in the P5 relay?

Attachments
Labels
  • Labels:
  • PowerLogic P5
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Arun-kumar_PS
Lt. Commander Arun-kumar_PS Lt. Commander
Lt. Commander

Posted: ‎2025-02-11 02:55 AM

1 Like
0
585
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-11 02:55 AM

Hello @sungur 

Normally, a instantaneous overcurrent / earth fault element is used for high impedance protection

As described in the application note, Overcurrent element I>1 can be used for 87BB. 

There is no specific 87BB element. 

 

Regards,

Arun

See Answer In Context

Attachments
Reply
Reply 1
Arun-kumar_PS
Lt. Commander Arun-kumar_PS Lt. Commander
Lt. Commander

Posted: ‎2025-02-11 02:55 AM

1 Like
0
586
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-11 02:55 AM

Hello @sungur 

Normally, a instantaneous overcurrent / earth fault element is used for high impedance protection

As described in the application note, Overcurrent element I>1 can be used for 87BB. 

There is no specific 87BB element. 

 

Regards,

Arun

Attachments
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now