RS-485 - 2-wire

Power Monitoring and Energy Automation NAM

This forum is created for the exchange of information and open dialogue regarding electrical power monitoring and energy automation products and services. Participants will have access to downloadable material as well as chat opportunities with subject matter experts.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution NEMA
  • Power Monitoring and Energy Automation NAM
  • RS-485 - 2-wire
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
5
Michael_Neas
Ensign Michael_Neas Ensign
3
Robert_Lee
Admiral Robert_Lee Admiral
2
sesa29811
Crewman sesa29811 Crewman
1
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Power Monitoring and Energy Automation NAM
Beeshive
Crewman Beeshive
Crewman

Posted: ‎2024-12-23 01:34 PM

0 Likes
1
332
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-23 01:34 PM

RS-485 - 2-wire

I hope that I'm not the only one that gets driven around the bend by the different RS-485 implementations of RS-485 2-Wire.

 

I have switchgear that consists of MasterPact breakers with Micrologic 5.0A / Micrologic 6.0P and PM800 power meters.

All of the devices are set up for 2-Wire 9600-8-N-1.

Almost all of the other RS-485 networks for Modbus and Bacnet in this facility are wired up using Belden 3106A 1.5 pair twisted wire with shield. On these networks, which is mainly ABB and Schneider VFDs and Belimo actuators, the twisted pair is the Data A- & B+ with the single conductor as the common and the shield is only grounded at one end of the loop.
The RS-485 network for the Micrologics and the PM800 is using the 1.5 pair twisted with shielded. The twisted pair is used for data, the single conductor is not used for common, and the shield connects to all of the devices and is earthed at both ends of the run.

I am currently having issues with a group of PM800s that are at the end of a 300' loop that has the monitoring front end in one building and the PM800s are in an other building.
Am I asking for trouble with the shield earthed at both ends? Yes the buildings share a common earth bond, but still. And why do the Micrologic 5.0A and 6.0P manuals call for the shield to be used as the common?

Attachments
Labels
  • Labels:
  • Medium Voltage (MV) Relays & Meters
  • SCADA
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2025-01-07 09:58 AM

1 Like
0
256
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-07 09:58 AM

Hello @Beeshive 

 

I cannot speak to the Micrologic as I have no experience with those devices. For the PM800 meters, shield earthed at both ends could be a source of grounding loops if the earth of the shield is connected to the earth of the control power. I do not have access to a meter right now to test but you could try measure the resistance between control power ground the RS-485 shield connectors.


PM800 meters are fairly old at this point. Have you looked into the PM5000 or PM8000 as replacements?

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of