High End Platform (ION9000, ION7400) v3.0.0 FAQ - User Accounts and Legacy Security

Power Monitoring and Energy Automation NAM

This forum is created for the exchange of information and open dialogue regarding electrical power monitoring and energy automation products and services. Participants will have access to downloadable material as well as chat opportunities with subject matter experts.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution NEMA
  • Power Monitoring and Energy Automation NAM
  • High End Platform (ION9000, ION7400) v3.0.0 FAQ - User Accounts and Legacy Security
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
7
Michael_Neas
Ensign Michael_Neas Ensign
3
Robert_Lee
Admiral Robert_Lee Admiral
2
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Power Monitoring and Energy Automation NAM
Start a Topic
Chris_Kerr
Ensign Chris_Kerr Ensign
Ensign

Posted: ‎2021-02-12 03:49 PM . Last Modified: ‎2021-02-12 03:51 PM

0 Likes
0
1890
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-02-12 03:49 PM . Last Modified: ‎2021-02-12 03:51 PM

High End Platform (ION9000, ION7400) v3.0.0 FAQ - User Accounts and Legacy Security

From our FAQ database:

High End Platform (ION9000, ION7400, PM8000) Firmware v3.0.0 FAQ - User Accounts and Legacy Security...

 

Issue
Questions regarding the V3.0.0 firmware release for HEP meters

Product
ION9000, ION9000T, PM8000, ION7400

Resolution
If using Power Monitoring Expert with the v3.0.0 meter, please refer to FA409899 for more information
If using ION Setup with v3.0.0 meter, please refer to FA409930 for more information.

Upgrades:
Q: What is the minimum version of Firmware required on the meter to upgrade to v3.0.0?
A: Firmware version 2.1.0 or greater required on the meter to upgrade to v3.0.0

Q: What is the minimum version of ION Setup required to upgrade the meter?
A: Recommend v3.2.20218.01 or later versions. See FA212816 for links to the latest version

Q: What happens if I use an old version of ION Setup to upgrade my meter
A: Depending on the age of ION Setup, when selecting the .ZIP file, ION Setup will provide a warning to upgrade the version of ION Setup before starting the upgrade. However if the .upx file is sent without the zip file, ION Setup cannot check what version of ION Setup is required. After ION Setup sends the upgrade file, ION Setup will try to program the meter and send saved register information like accumulated energy. However there will be an error and ION Setup will not be able to write the values. Register information data loss will occur. The firmware will be upgraded however the meter will not have the template loaded.

Q: Can ION Setup detect a new version of software is required to upgrade the meter?
A: If using the ZIP file, ION Setup is able to read the minimum required software version, however if just using the .upx file, ION Setup cannot determine the minimum software version.

Q: Can I downgrade my meter to a previous version of firmware?
A: No, meter can not be downgraded.

Q: Can I update my meter if using ION over modbus
A: Sometimes, refer to FA410328 for more information. If using a HEP meter as a modbus gateway, the upgrade via ION over Modbus may fail. Other gateway devices like EGX may work. Note the upgrade over serial will be very slow and not recommended. Recommend upgrading meter via Ethernet connection.

Q: Is there a new template with this firmware upgrade
A: No, there is no new template with this firmware

Q: Where can I find instructions on how to upgrade the meter:
A: Go to se.com, search for the document "7EN72-0206-00"

Security:
Q: What security options exist in the meters before v3.0.0 Firmware?
A: Standard (default): Front panel password with no user information required when writing to the meter. Anonymous access can read from the meter
Advanced Security: Username and password required to read or write to the meter
No security: No username or password required to read or write to the meter

Q: What security options are available with meters running v3.0.0 Firmware?
A: Advanced Security: Same as before
Legacy security support: Interim option where requests without a user name supplied will be mapped to permissions of User1 in the meter 

Q: What is the default security setting from the factory on v3.0.0 meters
A: Legacy security support is enabled, User1 has full permissions and a password of 0

Q: Can I still access my meter's web pages using http?
A: If web access setup register is set to HTTP With redirect to HTTPS, connecting to the meter's web page will be automatically redirected to https

Q: What happens to Security User Modules if the meter is upgraded while standard security is enabled?
A: The existing modules are deleted and User1 module created.

Q: Can I still use ION over Modbus if the Modbus Map Access is set to None?
A: Yes, still possible to communicate to meter with ION over modbus

User accounts:
Q: What user do I need to use we connecting to the meter's Web page?
Ans: If Legacy Security Support is enabled, meter model can still be used example 9000. If LSS is disabled, the user will need to be something like user1. Any browser that has cached user name and password in the browser will need to be updated.

Q: What user to login with when using SSH to access terminal?  
A: Default is User1 provided the user has permissions to access the meter. Meter model number can only be used if Legacy Security Support is enabled

Q: Can a user change permissions of the account used to connect to the meter?
A: No, I user cannot change permissions of the account connected to the meter.

Passwords
Q: With v3.0 firmware, can I change the password from the front panel
A: No, the option to change password from the front panel has been removed.

Q: What is the maximum password complexity available?
A: Refer to FA279497 for more information on password complexity

Q: With v3.0.0 firmware, can a user change the password of the account used to connect to the meter
A: Yes the password can be updated

Q: Can I use an alphanumeric password for User1 with Legacy security support enabled
A: Nothing in the meter will prevent this password however some software will not be able to talk to the meter as standard security was assumed to be numeric only and some software will enforce this limitation when entering in a password.

Labels
  • Labels:
  • ION 7400
  • ION 9000
  • power monitoring expert
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore