Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-08-18 09:38 PM
for 11/.4kv transformer the lv is ungrounded star what is the effect of first line to ground fault on the ....?
1- 3 phase load (motor).
2- single phase line to neutral loads on healthy phases?
3- single phase line to neutral loads on faulted phase?
by another way what is the effect of fault on 1, 2 , 3 and motor loads according to attached pic?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-09-15 06:59 AM . Last Modified: 2025-09-15 07:00 AM
Hello @zezo ,
Because you are in ungrouded system, any first ground fault will not impact your process and operator security. On insulated network, earth leakage current cannot loop through ground to the MV/LV transformer (Iground will be very low).
In case of a 2nd ground fault on another phase, there is a risk (for peoples and processes). You need to install:
For you reference:
Regards,
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-09-15 06:59 AM . Last Modified: 2025-09-15 07:00 AM
Hello @zezo ,
Because you are in ungrouded system, any first ground fault will not impact your process and operator security. On insulated network, earth leakage current cannot loop through ground to the MV/LV transformer (Iground will be very low).
In case of a 2nd ground fault on another phase, there is a risk (for peoples and processes). You need to install:
For you reference:
Regards,