ZSI compatibility P frame downstream of a H Frame
  • Power Distribution IEC
  • ZSI compatibility P frame downstream of a H Frame
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
80
J_Travostino
Sisko J_Travostino Sisko
70
Avila.Andres
Crewman Avila.Andres
Crewman
Posted: ‎2024-02-01 04:31 PM . Last Modified: ‎2024-02-01 04:32 PM
1554
Hi! Currently on the jobsite we have a Powerpact P Frame breaker with a micrologic 5.0 P as a downstream device for a Powerpact L Frame breaker with a micrologic 5.3 E.
Since the ZSI module LV434212 is required for each Masterpact NT/NW, PowerPact P/R, or Compact NS circuit breaker that is connected upstream of Powerpact H/J/L or Compact NSX circuit breaker,
Is the opposite also true? If I have an H frame connected upstream of a Powerpact P/R, do I also need a ZSI Module?
Thank you,
  • How to
  • Powerpact
  • ZSI
Gregoire_Brun
Commander
Posted: ‎2024-02-06 12:29 AM
How is it possible to have a Powerpact L 400A upstream and a Powerpact P 800A downstream ?
For thermal / câble protection , it look not correct and maybe dangerous !
Our recomendation is to have a smaller or equivalent device dowstream of all breakers. With natural selectivity function on the breaker, it's the powerpact L witch will trip all the time am first. the P breaker will not protect anythink.
So why you choice a powerpact P for downstream network?
Correct me if I'm wrong....
Gregoire
Gregoire Brun
Breaker Product Expert
Replies 4
S-W
Commander S-W Commander
Commander
Posted: ‎2024-02-02 12:37 AM
Hi @Avila.Andres, Could you upload the images again? It's not showing up anymore. Just wanna make sure we understand your case correctly. Thank you.
Avila.Andres
Crewman
Posted: ‎2024-02-02 12:44 PM
I sure can, thank you for taking the time.
The Downstream device is a P Frame breaker with a micrologic 5.0 P while the Upstream breaker is an H Frame with a micrologic 5.3 E.
Avila.Andres
Crewman
Posted: ‎2024-02-02 12:52 PM
Following this table it seems there is no compatibility from a Downstream P frame to an Upstream L frame?
Gregoire_Brun
Commander
Gregoire
Gregoire Brun