Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-02-01 04:31 PM . Last Modified: 2024-02-01 04:32 PM
Hi! Currently on the jobsite we have a Powerpact P Frame breaker with a micrologic 5.0 P as a downstream device for a Powerpact L Frame breaker with a micrologic 5.3 E.
Since the ZSI module LV434212 is required for each Masterpact NT/NW, PowerPact P/R, or Compact NS circuit breaker that is connected upstream of Powerpact H/J/L or Compact NSX circuit breaker,
Is the opposite also true? If I have an H frame connected upstream of a Powerpact P/R, do I also need a ZSI Module?
Thank you,
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-02-06 12:29 AM
How is it possible to have a Powerpact L 400A upstream and a Powerpact P 800A downstream ?
For thermal / câble protection , it look not correct and maybe dangerous !
Our recomendation is to have a smaller or equivalent device dowstream of all breakers. With natural selectivity function on the breaker, it's the powerpact L witch will trip all the time am first. the P breaker will not protect anythink.
So why you choice a powerpact P for downstream network?
Correct me if I'm wrong....
Gregoire
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-02-02 12:37 AM
Hi @Avila.Andres, Could you upload the images again? It's not showing up anymore. Just wanna make sure we understand your case correctly. Thank you.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-02-06 12:29 AM
How is it possible to have a Powerpact L 400A upstream and a Powerpact P 800A downstream ?
For thermal / câble protection , it look not correct and maybe dangerous !
Our recomendation is to have a smaller or equivalent device dowstream of all breakers. With natural selectivity function on the breaker, it's the powerpact L witch will trip all the time am first. the P breaker will not protect anythink.
So why you choice a powerpact P for downstream network?
Correct me if I'm wrong....
Gregoire
Link copied. Please paste this link to share this article on your social media post.