Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-09-06 04:21 AM
I provide coordinated settings for VIP 400 relays. Occasionally I would like to use the Instantaneous option for the I>>> stage. The availability of the Instantaneous option seems to be factory set.
How can I know, in advance, if the Instantaneous option (MIN TRIP TIME : OFF) will be available to the engineer entering the settings into the relay? For each relay I am aware of the SE circuit breaker model the relay is connected to but do not have access to the relay.
When and how can I request the 'MIN TRIP TIME' is set to 'off' to enable the Instantaneous options?
Any help that enables me to answer these two questions would be greatly appreciated.
Thank you!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-10-11 11:06 PM
Hi Bweener,
To change the setting of 'MIN TRIP TIME', first you need to activate "CB CUSTOM" display and then can review 'MIN TRIP TIME' setting. Press the "Conform enter" Key and hold on for more than 7s, this setting is allowed to change. You can check the attachment.
BR,
Jinlei XING
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-10-10 03:13 AM
@Pete_Vivers hi, could anybody from your team take care about this question related to VIP400?. Thanks a lot for your support.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-10-11 11:06 PM
Hi Bweener,
To change the setting of 'MIN TRIP TIME', first you need to activate "CB CUSTOM" display and then can review 'MIN TRIP TIME' setting. Press the "Conform enter" Key and hold on for more than 7s, this setting is allowed to change. You can check the attachment.
BR,
Jinlei XING