NS1600N withdrawable circuit breaker stab tempreture

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • NS1600N withdrawable circuit breaker stab tempreture
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
71
J_Travostino
Sisko J_Travostino Sisko
70
S-W
Commander S-W Commander
66
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Solved
Lyndseybielich..
Crewman Lyndseybielich..
Crewman

Posted: ‎2022-10-09 07:43 AM

0 Likes
5
1298
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-09 07:43 AM

NS1600N withdrawable circuit breaker stab tempreture

Good Day, 

 

Does anyone know the temperature of the Stab on a NS1600N withdrawable circuit breaker

Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Christian_Bach
Lt. Commander Christian_Bach Lt. Commander
Lt. Commander

Posted: ‎2022-10-11 05:15 AM

In response to Lyndseybielich..
0 Likes
2
1250
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-11 05:15 AM

Good day,

 

The standard IEC60947-1  states 70K temp rise for silver plated connections, which is the case on NS1600, for a maximum reference temperature of 40°C around the CB :

 

"The ambient air temperature does not exceed +40 °C and its average over a period of 24 h
does not exceed +35 °C."

 

This requirement is given in free air, with the cable / bars sections stated by the standard (2 bars of 100mm x 5mm for 1600A).

 

Best regards,

Christian

 

 

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Christian_Bach
Lt. Commander Christian_Bach Lt. Commander
Lt. Commander

Posted: ‎2022-10-11 06:17 AM

In response to Lyndseybielich..
0 Likes
0
1242
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-11 06:17 AM

Maybe my message was not clear enough : the temp rise allowed is 70K on the customer connections, under the conditions of the product standard (vertical mounting, in free air with the requested cross sections).

 

This is for "new state" product, after tests the limit is raised to 80K as per IEC60947-2. 

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Christian_Bach
Lt. Commander Christian_Bach Lt. Commander
Lt. Commander

Posted: ‎2022-10-09 11:25 PM

1 Like
4
1277
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-09 11:25 PM

Good day,

 

Could you please clarify the points below ;

- is your question related to UL489 or IEC ?

- do you mean stabs on the circuit breaker or on the chassis busbars connection ?

 

Best regards,

Christian

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Lyndseybielich..
Crewman Lyndseybielich..
Crewman

Posted: ‎2022-10-10 03:16 AM

In response to Christian_Bach
0 Likes
3
1266
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-10 03:16 AM

Good Day,

 

We are looking for the heat temperature on the stab of the NS1600N breaker as per the IEC specifications. 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Christian_Bach
Lt. Commander Christian_Bach Lt. Commander
Lt. Commander

Posted: ‎2022-10-11 05:15 AM

In response to Lyndseybielich..
0 Likes
2
1251
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-11 05:15 AM

Good day,

 

The standard IEC60947-1  states 70K temp rise for silver plated connections, which is the case on NS1600, for a maximum reference temperature of 40°C around the CB :

 

"The ambient air temperature does not exceed +40 °C and its average over a period of 24 h
does not exceed +35 °C."

 

This requirement is given in free air, with the cable / bars sections stated by the standard (2 bars of 100mm x 5mm for 1600A).

 

Best regards,

Christian

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Lyndseybielich..
Crewman Lyndseybielich..
Crewman

Posted: ‎2022-10-11 06:11 AM

In response to Christian_Bach
0 Likes
1
1244
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-11 06:11 AM

Not referring to the ambient temperature, I would like the actual temperature rise on the sub of the busbar coming out the breaker. 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Christian_Bach
Lt. Commander Christian_Bach Lt. Commander
Lt. Commander

Posted: ‎2022-10-11 06:17 AM

In response to Lyndseybielich..
0 Likes
0
1243
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-11 06:17 AM

Maybe my message was not clear enough : the temp rise allowed is 70K on the customer connections, under the conditions of the product standard (vertical mounting, in free air with the requested cross sections).

 

This is for "new state" product, after tests the limit is raised to 80K as per IEC60947-2. 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of