UL1699 certification for AFDD
  • Power Distribution IEC
  • UL1699 certification for AFDD
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
80
J_Travostino
Sisko J_Travostino Sisko
70
Acti9 Arc Fault Detection Devices
Gingko_Elec
Lieutenant JG Gingko_Elec
Lieutenant JG
Posted: ‎2020-03-27 05:02 AM . Last Modified: ‎2020-11-25 03:53 AM
3985
Could you tell me please if, in UL countries, Arc Fault detection Devices need to be UL1699 certified?
  • Products
  • Safety - Electrical Fire Prevention
  • Safety - People Safety
MathieuGuillot
Lieutenant MathieuGuillot Lieutenant
Lieutenant
Posted: ‎2020-04-02 08:48 AM
1
3960
In "UL" countries,  AFDD is called "Arc fault Circuit Interruptor" and the related standard is indeed UL 1699.
In the US the installation of this solution is required for some circuits by  the National Electric Code (NFPA70A :Clause 210.12), in that case the product shall be a "listed" AFCI, meaning it shall be compliant to UL 1699.
If the installation of this solution is not based on the NEC requirement, in particular in "UL" country that is not the US, an IEC AFDD according to IEC/EN 62606 could be used as well if IEC/EN product are accepted.
Does it answer the question ?
MathieuGuillot
Lieutenant
1
3961
Gingko_Elec
Lieutenant JG
Posted: ‎2020-04-06 06:22 AM
In response to MathieuGuillot
Yes, thank you Mathieu!