Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-03-26 09:34 AM . Last Modified: 2020-11-25 03:52 AM
Hello,
I couldn't understand from webinar what do with molded case breakers, in case of distributed neutral (4 wires) installation.
Should we add a 4 poles Vigi with adaptor on the triple pole Compact NSX?
Thanks for giving clarity on this specific case.
Best
Espe
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-03-31 06:35 AM
Hello,
In 3 Phases + Neutral system the RCD shall measure the current of 3 phases and Neutral. If in this type of system a 3 poles ComPact NSX is used and RCD funciton is expected, three options are possible :
Note : Today there is no equivalent of "Vigi 4P/3P adpator" for Micrologic Vigi 4.x / 7.x. If you consider this is a concern don't hesistate to provide feedback.
Regards
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-03-31 06:35 AM
Hello,
In 3 Phases + Neutral system the RCD shall measure the current of 3 phases and Neutral. If in this type of system a 3 poles ComPact NSX is used and RCD funciton is expected, three options are possible :
Note : Today there is no equivalent of "Vigi 4P/3P adpator" for Micrologic Vigi 4.x / 7.x. If you consider this is a concern don't hesistate to provide feedback.
Regards
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-04-06 06:45 AM
Thanks Mathieu,
At this point I can implement at least one option among 3 ones in different cases I met up to now.
Best
Espe