Secure against over temperature in electrical switchboards

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • Secure against over temperature in electrical switchboards
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
80
J_Travostino
Sisko J_Travostino Sisko
70
View All

Recommended Forums

  • Comunidade de Soluções Elétricas

  • Expert on Demand for Standards & Regulations

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Start a Topic
Solved
Esperanto
Lieutenant JG Esperanto
Lieutenant JG

Posted: ‎2019-04-02 03:00 AM . Last Modified: ‎2019-08-09 03:46 AM

2 Likes
3
4556
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-04-02 03:00 AM . Last Modified: ‎2019-08-09 03:46 AM

Secure against over temperature in electrical switchboards

Hello all, 

 

Just discovering this new Community at the time I have to implement a switchboard within a high temperature environment (40°C), I am looking for guidelines to relevantly design this switchboard against its demanding environmental conditions.

 

Would anyone have any experience in this topic and could point at simple and relevant design and implementation recommendations?

 

Thanks in advance.

Espe

  • Tags:
  • Switchboard temperature
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
PascalL
PascalL Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2019-04-02 07:17 AM

6 Likes
0
4538
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-04-02 07:17 AM

Hello,

 

Following your question, please find some inputs to help you in your specification: ambient temperature 40°C to low voltage switchboard installation.

Based on the standard to the type of Assembly, IEC61439-1/2 the reference to the external ambient temperature is 35°C, so your personal constrain is not so high and so far,

I don’t know if your Assembly switchboard is compliance with IEC61439, but I hope so, if it is the case the Original Manufacturer shall be able to produce the rated current at different temperatures, and to different type of IP level which influence the convection and so the rating of the component installed into the enclosure. 

 

The  aim of IEC61439 is to propose an Assembly with a high level of Electrical Safety and Power availabily.

That mean, when you get an IEC61439 Assembly you get verified performances coming from an Original Manufacturer responsible of the Design verifications and from an Assembly Manufacturer responsible of the routine verification.

The sums of those verification drive to an Assembly equipment with performances verified and certified to the full life of usage of an Assembly.

For example, the IEC61439 ensure the thermal stability and reliability, the rated current and the short-circuit withstand stress, all the clearances and creepage distances to the insulation coordination.

This high level of performances is the guarantee to avoid safety risk to people protection and loss of service continuity.

I use the opportunity to encourage you to have a look on the different blog articles referring to the same kind of topics most precisely:

 

https://blog.schneider-electric.com/power-management-metering-monitoring-power-quality/2018/07/10/wi...

 

And a small video

https://www.bing.com/videos/search?q=61439+schneider+electric+india&&view=detail&mid=5FDBFF3CA4F013E...

 

Best regards,

LV system inst. expert - Standardization officer

pascal.lepretre@se.com

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
PascalL
PascalL Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2019-04-02 07:17 AM

6 Likes
0
4539
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-04-02 07:17 AM

Hello,

 

Following your question, please find some inputs to help you in your specification: ambient temperature 40°C to low voltage switchboard installation.

Based on the standard to the type of Assembly, IEC61439-1/2 the reference to the external ambient temperature is 35°C, so your personal constrain is not so high and so far,

I don’t know if your Assembly switchboard is compliance with IEC61439, but I hope so, if it is the case the Original Manufacturer shall be able to produce the rated current at different temperatures, and to different type of IP level which influence the convection and so the rating of the component installed into the enclosure. 

 

The  aim of IEC61439 is to propose an Assembly with a high level of Electrical Safety and Power availabily.

That mean, when you get an IEC61439 Assembly you get verified performances coming from an Original Manufacturer responsible of the Design verifications and from an Assembly Manufacturer responsible of the routine verification.

The sums of those verification drive to an Assembly equipment with performances verified and certified to the full life of usage of an Assembly.

For example, the IEC61439 ensure the thermal stability and reliability, the rated current and the short-circuit withstand stress, all the clearances and creepage distances to the insulation coordination.

This high level of performances is the guarantee to avoid safety risk to people protection and loss of service continuity.

I use the opportunity to encourage you to have a look on the different blog articles referring to the same kind of topics most precisely:

 

https://blog.schneider-electric.com/power-management-metering-monitoring-power-quality/2018/07/10/wi...

 

And a small video

https://www.bing.com/videos/search?q=61439+schneider+electric+india&&view=detail&mid=5FDBFF3CA4F013E...

 

Best regards,

LV system inst. expert - Standardization officer

pascal.lepretre@se.com

Reply

Link copied. Please paste this link to share this article on your social media post.

Enrique
Enrique Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2019-04-03 06:23 AM

0 Likes
0
4522
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-04-03 06:23 AM

Hello,

We have great experience on design / build / operate panels in the regions where temperatures are up to 55º, like Middle East. I would recommend you to contact the local Schneider team there to get a brief on the key topics. Let me know if you need more details as names of people.

Thanks,

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2019-07-22 11:27 PM

0 Likes
0
4017
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-07-22 11:27 PM

 
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore