TRIP CIRCUIT SUPERVISION
  • Power Distribution IEC
  • TRIP CIRCUIT SUPERVISION
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
80
J_Travostino
Sisko J_Travostino Sisko
70
Himdad
Himdad
Cadet
Posted: ‎2023-01-22 05:08 AM
3161
Hi, I am seeking your technical support regarding the application of the TCS function in LV system, as we are going to install a TCS function in our LV switchgear to protect the operation system, but we see that in some of the ACBs have an internal trip units ensure high-reliability thanks to an electronic circuit that periodically checks the continuity of internal connections, such as trip coil, rating plug, and each current sensor (ANSI 74), hereby I am asking can we consider this unit working as a TCS function? or we must install a separate device to act as a TCS?
himdad bahri
Gregoire_Brun
Commander
Posted: ‎2023-01-23 01:07 AM
hello @Himdad
infernal connections checking are in place to garanty safety function of our breaker.
To check status of the breaker associate to a Scada or others, you can use BCM/BSCM to collect status of the Breaker (or classique OF SD contacts...)
Gregoire Brun
Breaker Product Expert
Replies 4
Gregoire_Brun
Commander
hello @Himdad
Gregoire Brun
Christian_Bach
Lt. Commander Christian_Bach Lt. Commander
Lt. Commander
Posted: ‎2023-01-23 01:11 AM . Last Modified: ‎2023-01-23 01:11 AM
3131
As Gregoire said, MasterPact MTZ is equipped of self diagnosis features.
When you mean TCS, are you looking for a specific standard or regulation ?
Christian
SK201171
SK201171 Cadet
Cadet
Posted: ‎2023-01-23 01:47 AM . Last Modified: ‎2023-01-23 01:49 AM
In response to Christian_Bach
Hi @Himdad & @Christian_Bach ,
TCS is Trip Circuit Supervision, primarily used in MV Circuit breaker to measure the control voltage flowing throwing through the opening circuit.
We have the feature to diagnose the Operating coil healthiness XF, MN in MTZ.
You shall use the below mentioned link to understand the features in MTZ
https://product-help.schneider-electric.com/ED/MTZ/Micrologic_X_User_Guide/EDMS/DOCA0102EN/DOCA0102x....
Baljit
Crewman Baljit Crewman
Crewman
Posted: ‎2023-01-23 02:57 PM
@Himdad - I believe you can consider the MTZ inbuilt Trip circuit supervision function as it complies to ANSI 74 requirements. See snippet in the attachment.