Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-09-23 10:13 AM
I'm trying to figure out what the single pole trip current should be, without actually testing the breaker. My brain wants to make the assumption 60amps total for all 3 legs (RMS sum) which would make each pole 20amps (1-1.5x based on trip curve), but I can't find this written down or fully described anywhere.
Anyone know the answer, or a link to a video where single pole tripping was tested?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-09-26 01:45 AM
hello @zerohourrct
On breaker QO360VH, Line Rated Current is 60A and this value is for each phase. it's a 3 x 60A
Best regards
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-09-26 03:16 AM
Hi @zerohourrct ,
If your question relates to short & long time protection, UL489 CBs are tested in single pole at a multiple of the rated current (60A here).
For example, 200% of 60A.
Christian
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-09-26 01:45 AM
hello @zerohourrct
On breaker QO360VH, Line Rated Current is 60A and this value is for each phase. it's a 3 x 60A
Best regards
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-09-26 03:16 AM
Hi @zerohourrct ,
If your question relates to short & long time protection, UL489 CBs are tested in single pole at a multiple of the rated current (60A here).
For example, 200% of 60A.
Christian