Single Pole trip current for QO360VH 3pole 60amp breaker

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • Single Pole trip current for QO360VH 3pole 60amp breaker
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
71
J_Travostino
Sisko J_Travostino Sisko
70
S-W
Commander S-W Commander
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Solved
zerohourrct
zerohourrct
Cadet

Posted: ‎2022-09-23 10:13 AM

0 Likes
2
993
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-23 10:13 AM

Single Pole trip current for QO360VH 3pole 60amp breaker

I'm trying to figure out what the single pole trip current should be, without actually testing the breaker. My brain wants to make the assumption 60amps total for all 3 legs (RMS sum) which would make each pole 20amps (1-1.5x based on trip curve), but I can't find this written down or fully described anywhere.

 

Anyone know the answer, or a link to a video where single pole tripping was tested?

Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Gregoire_Brun
Commander Gregoire_Brun Commander
Commander

Posted: ‎2022-09-26 01:45 AM

0 Likes
0
950
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-26 01:45 AM

hello @zerohourrct 

On breaker QO360VH, Line Rated Current is 60A and this value is for each phase. it's a 3 x 60A

 

Best regards

Gregoire Brun
Breaker Product Expert

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Christian_Bach
Lt. Commander Christian_Bach Lt. Commander
Lt. Commander

Posted: ‎2022-09-26 03:16 AM

0 Likes
0
938
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-26 03:16 AM

Hi @zerohourrct ,

 

If your question relates to short & long time protection, UL489 CBs are tested in single pole at a multiple of the rated current (60A here).

 

For example, 200% of 60A.

 

Christian

 

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Gregoire_Brun
Commander Gregoire_Brun Commander
Commander

Posted: ‎2022-09-26 01:45 AM

0 Likes
0
951
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-26 01:45 AM

hello @zerohourrct 

On breaker QO360VH, Line Rated Current is 60A and this value is for each phase. it's a 3 x 60A

 

Best regards

Gregoire Brun
Breaker Product Expert
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Christian_Bach
Lt. Commander Christian_Bach Lt. Commander
Lt. Commander

Posted: ‎2022-09-26 03:16 AM

0 Likes
0
939
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-26 03:16 AM

Hi @zerohourrct ,

 

If your question relates to short & long time protection, UL489 CBs are tested in single pole at a multiple of the rated current (60A here).

 

For example, 200% of 60A.

 

Christian

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login