Simplified reference electrical power distribution network configuration for a data center; by using Ecodial

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • Simplified reference electrical power distribution network configuration for a data center; by using Ecodial
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
80
J_Travostino
Sisko J_Travostino Sisko
70
View All

Recommended Forums

  • Comunidade de Soluções Elétricas

  • Expert on Demand for Standards & Regulations

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Start a Topic
Solved
Genghiz
Captain Genghiz Captain
Captain

Posted: ‎2020-11-25 12:11 AM . Last Modified: ‎2024-11-22 04:25 AM

2 Likes
4
3168
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-25 12:11 AM . Last Modified: ‎2024-11-22 04:25 AM

Simplified reference electrical power distribution network configuration for a data center; by using Ecodial

Introduction : 

The data center 'architecture model' is considered as a reference to understand the 'electrical equipment's and their characteristics in detail. However the 'electrical distribution' model network needs to be prepared then a design software is needed to do so.

 

Architectural Model :  

The enclosed image shows the 'main distribution board' of the data center. 

 

Data Center Project_Model.PNG

 

Solution : 

Here by considering the EcoStruxure Power Design - Ecodial INT version, we have prepared a sample project. This will present the basic representation of the electrical distribution network of a data center.

 

Project File : 

Here is the link to download the Ecodial Project File 

 

Points to be considered under the Ecodial Project :

  • The operating modes are considered to study the different operating conditions.
  • The HLLV transformer ratings is consider for it's Maximum (that is 3150 kVA), where as expectation was 3000 kVA
  • The LV Generator is represented in 2 numbers in parallel to meet the expected representation of 2500 kVA.
  • If required; the detailed consumption pattern (open and close) of the feeder needs to be considered under the operating modes.

 

Data Center_Project Model_EcodialData Center_Project Model_Ecodial

 

 

Labels
  • Labels:
  • Power Distribution Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Genghiz
Captain Genghiz Captain
Captain

Posted: ‎2020-12-01 12:03 AM

1 Like
0
3142
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-12-01 12:03 AM

Hello Jamillah,

Thanks for your comment. As requested, an option download the relevant "Ecodial Project File" is added to the above article. 

Thank you.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: ‎2020-11-25 08:40 PM

1 Like
0
3160
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-25 08:40 PM

hi Genghiz,

 

This is very nice. please share the ecodial project file if possible.

 

thanks,

Jamillah

Reply

Link copied. Please paste this link to share this article on your social media post.

Genghiz
Captain Genghiz Captain
Captain

Posted: ‎2020-12-01 12:03 AM

1 Like
0
3143
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-12-01 12:03 AM

Hello Jamillah,

Thanks for your comment. As requested, an option download the relevant "Ecodial Project File" is added to the above article. 

Thank you.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-03-05 12:36 AM

1 Like
0
2870
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-05 12:36 AM

Nice work Genghiz, Can you please update the link? Seems the file is not longer available.

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Genghiz
Captain Genghiz Captain
Captain

Posted: ‎2021-03-07 09:24 PM

0 Likes
0
2860
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-07 09:24 PM

Hello,

Thanks for your comments.

The link to download the file is updated, and I hope you should be able to access the file now.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.