An example for 'determining the smallest allowable cross-sectional area of circuit conductors.'
  • Power Distribution IEC
  • An example for 'determining the smallest allowable cross-sectional area of circuit conductors.'
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
78
J_Travostino
Sisko J_Travostino Sisko
70
S-W
Commander S-W Commander
67
Genghiz
Captain
Posted: ‎2020-11-09 11:59 PM . Last Modified: ‎2024-11-22 04:25 AM
1
3379
From the available inputs;
let us see how to determine the 'smallest allowable cross sectional area' of the circuit conductors.
Available inputs;
Load Current
200 A
THDi
48 %
Conductor Insulation*
XLPE
Conductor Type
Multi-Core Cable
Conductor Material*
Copper
Installation
Directly in Ground
Soil Resistivity*
2 Km/w
Soil Temperature*
40*C
*Some of the inputs are assumed to provide in this example; and they were neither received from the user, nor from the environment.
Procedure:
  • Determinant conductor : Neutral
          As the THDi is > 33 % (that is THDI = 48 %). So, the Size-determining" live conductor is Neutral
  • Neutral Current               :  3 × 0.48 × 200 = 288 A
  • Correction factor K3       : The factor based on the overload protection device.
           This circuit is assumed to be protected by the circuit-breaker.
           So that the K3 =1.0
  • F1 Temperature              : Table B.52.15
          For 40°C and with the insulation XLPE. F1 = 0.85
  • Installation method       : 72        (Sheathed single-core or multi-core cables direct in the ground - without added mechanical protection) Reference method          : D2
  • F2 Group                          : Table B.52.18
          There is no additional touching circuits i.e. total no. of circuits is 1
          F2group = 1.00
  • Correction factor F3       : Table (E.52.1)
          THDI >45 % = THDI = 48 %  à f3NeutralTHDI = 1.00
  • F3RSoil                              : Table B.52.16
           Installation method = in Ground -> Rth = 2.0 K.m/w
           f3RthSoil = 1.12
  • K user = 1.0
Correction factor f
f = 0.85 × 1.00 × 1.00 × 1.05 × 1.00 = 0.952
The overall correction factor is determined by multiplying all 'the available correction factors."
Theoretical Iz’                 = (K3 x IB) / (F x N live) = (1.0 x 288) / (0.952 x1) = 302.52 A = 303 A
The conductor selection is done from the given Table B.52.5 Column 8
185 mm2 will be able to carry 324 Amps
240 mm2 will be able to carry 375 Amps
Considering the +5% of tolerance, It would be recommended to consider the size as 185 mm²
K3(Correction Factor based on Protection Device)
1
F1(Correction Factor based on Temperature)
0.85
F2(Correction Factor based on Group of conductors)
1
F3(Correction Factor based on THDi)
1
F3(Correction Factor based on Soil Resistivity)
1.05
K user(Correction Factor defined by the user)
1
Iz’(A) Theoretical
303 A
Iz (A) considered from the table
324 A
Theoretical cross sectional area  Ph (mm²)
1 x 185   mm²
Theoretical cross sectional area Neutral (mm²)
1 x 185   mm²
Theoretical cross sectional area PE (mm²)
1 x 95   mm²
  • Power Distribution Software
dkpElect
Crewman dkpElect
Crewman
Posted: ‎2021-06-26 05:32 AM
That's really informative answer.
Thanks.
dkpElect
Crewman dkpElect
Crewman
Thanks.