Power Distribution and Digital Support
Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-04-11 06:16 PM . Last Modified: 2024-11-22 04:25 AM
Can Schneider Online tools support for Selectivity Curve of 2 Generator Breakers sharing 1 Big Load?
Example; 2 x 400kW Generators supply to 1 x 600kW Thruster VFD.
Generator Breakers are NT08H1, Micrologic 5.0 and Feeder ACB is NT12H1, Micro Logic 2.2
Upstream breakers are smaller than downstream breaker.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-07-03 05:22 AM
Hello Nyein Chan,
Thanks for reaching this forum.
The selectivity study by keep upstream smaller (<) than downstream will not be a valid combination.
Regards,
Team - Ecodial Expert Support
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-07-03 05:22 AM
Hello Nyein Chan,
Thanks for reaching this forum.
The selectivity study by keep upstream smaller (<) than downstream will not be a valid combination.
Regards,
Team - Ecodial Expert Support
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-07-03 05:26 AM
Hello Nyein Chan,
There is an additional information, that needs to be considered while doing this kind of design.
During the normal operation, it seems both the "sources" are sharing the load.
However, in a worst-case scenario, only one of them need to manage the load.
So, it's size will not be enough.
Regards,
Team - Ecodial Expert Support.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.