PE conductor size for TT system

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • PE conductor size for TT system
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
71
J_Travostino
Sisko J_Travostino Sisko
70
S-W
Commander S-W Commander
67
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Solved
kk_bb
kk_bb
Cadet

Posted: ‎2024-04-25 02:15 PM . Last Modified: ‎2024-11-22 04:25 AM

0 Likes
4
786
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-25 02:15 PM . Last Modified: ‎2024-11-22 04:25 AM

PE conductor size for TT system

Hello Everyone,

 

I'm using ecostruxure power design tool for my system. The problem is it always size the PE conductor following the rule of (half size of main conductor), although the earth fault current doesn't exceed 11A. As the earthing system is a TT system with a fault loop impedance of 20 ohm. So, isn't sizing as per the adiabatic equation available within the software.

 

Thanks in advance for your help

Attachments
Labels
  • Labels:
  • Power Distribution Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Genghiz
Captain Genghiz Captain
Captain

Posted: ‎2024-04-30 12:00 AM

0 Likes
0
750
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-30 12:00 AM

Hello,

Thanks for reaching the EPD FORUM.

 

The cable (conductor sizing) on the EPD Ecodial is based on the IEC standard (IEC 60364-5-52 & 54).

The sizing of protective earth (PE) conductor is specific and half of the ‘live conductor.’

Table 54 F.png

 

Thanks & Regards,

Team - Ecodial Expert Support

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Genghiz
Captain Genghiz Captain
Captain

Posted: ‎2024-04-30 12:00 AM

0 Likes
0
751
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-30 12:00 AM

Hello,

Thanks for reaching the EPD FORUM.

 

The cable (conductor sizing) on the EPD Ecodial is based on the IEC standard (IEC 60364-5-52 & 54).

The sizing of protective earth (PE) conductor is specific and half of the ‘live conductor.’

Table 54 F.png

 

Thanks & Regards,

Team - Ecodial Expert Support

Reply

Link copied. Please paste this link to share this article on your social media post.

kk_bb
kk_bb
Cadet

Posted: ‎2024-07-14 01:22 AM

0 Likes
0
620
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-14 01:22 AM

Thanks for your reply, and sorry for my late response. 

 

Thanks for the attached excerpt above, but it seems that it is extracted from an old version of IEC. As the updated IEC 60364-5-54 states that you can use the above table in case you do not use the adiabatic equation. The IEC even states that the protective conductor cross section shall not exceed 25mm2 for copper conductor and 35mm2 for aluminum conductor

Screenshot 2024-07-14 112052.pngScreenshot 2024-07-14 112216.png

 

Thanks and Best Regards

Reply

Link copied. Please paste this link to share this article on your social media post.

Genghiz
Captain Genghiz Captain
Captain

Posted: ‎2024-07-15 10:01 PM

0 Likes
0
616
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-15 10:01 PM

Thanks for your comments.

Can you please provide the extract from the IEC standard on this point.

 

The expectation is not yet clear...

The size of the PE conductor provided by the software is higher or smaller than the expected.? kindly please comment.

 

-Team Ecodial Expert Support.

Reply

Link copied. Please paste this link to share this article on your social media post.

kk_bb
kk_bb
Cadet

Posted: ‎2024-07-18 01:06 AM

0 Likes
0
599
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-18 01:06 AM

Thanks for your reply.

 

I already shared an extract above in my comment (IEC 60384-5-54:2011- clause 543.1) which states that you can use the adiabatic equation in 543.1.2 for sizing the protective conductor. It even states that in TT system (which is my case) the protective conductor size shall not exceed 25mm2 for copper and 35mm2 for aluminum (refer to 543.1.1 shown above).

 

Back to my case, I have a TT system where the fault current does not exceed 11.5A, hence it is enough to have a protective conductor of 4mm2 ( using the adiabatic equation), however the software also propose half size of the main conductor which way more than enough. Refer to the attached photos in my original post.

 

Thanks and best regards.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of