NW 50 H1 Breaker not closing.

Power Distribution and Digital

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

alungalsanthosh
Cadet

NW 50 H1 Breaker not closing.

Breaker not closing, Motor charged but indication showing un charge, charging motor circuit is open, charging handle not engaged. If press the close button by manual no action. Please advise the further trouble shooting, and how to release the spring charging and reset the mechanism.

Tags (1)
1 Reply 1
Christian_Bach
Lieutenant Lieutenant
Lieutenant

Re: NW 50 H1 Breaker not closing.

Hello @alungalsanthosh ,

 

A few questions :

 

What is exactly the state of the front indicator ?

- Discharged

- Charged "Not OK"

- Charged OK

 

What happens if you try charging the mechanism by handle ?

 

Alternately, did you investigate the following points :

- interlocking ?

- MN shunt trip coil not powered ?

- Trip indicator not resetted ?

 

Thanks,

Christian

 