Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.
Search in
Posted: 2022-07-11 03:09 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-07-11 03:09 AM
Good day to all,
Could you please clarify if IEC 61439 recognizes Aluminium as a conductor?
If yes then what are the temperature rise criteria limits defined for aluminium to aluminium joints?
Thanks!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-07-12 12:58 AM . Last Modified: 2022-07-15 07:15 PM
The IEC61439-1; edition 3 was published in May 2020 which recognizes Aluminium as conductor with well defined temperature rise criteria limits - 55K for untreated Aluminium to Aluminium Joints
However there will be no significant impact on the existing solutions that are complying to earlier edition 2 except on the temperature rise criteria's for Aluminium conductor. A maximum temperature-rise of 55 K for bare (uncoated) Aluminium busbars and conductors (Al-Al joint) shall not exceed, to ensure safety & performance of the solution over a prolonged duration of service.
Also attaching excerpts of IEC 61439 Ed. 3, Table 6 - Temperature-rise limits (9.2) for your ready reference.
Thanks,
Nitin Khare
Offer Marketing
EDN
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-07-12 12:58 AM . Last Modified: 2022-07-15 07:15 PM
The IEC61439-1; edition 3 was published in May 2020 which recognizes Aluminium as conductor with well defined temperature rise criteria limits - 55K for untreated Aluminium to Aluminium Joints
However there will be no significant impact on the existing solutions that are complying to earlier edition 2 except on the temperature rise criteria's for Aluminium conductor. A maximum temperature-rise of 55 K for bare (uncoated) Aluminium busbars and conductors (Al-Al joint) shall not exceed, to ensure safety & performance of the solution over a prolonged duration of service.
Also attaching excerpts of IEC 61439 Ed. 3, Table 6 - Temperature-rise limits (9.2) for your ready reference.
Thanks,
Nitin Khare
Offer Marketing
EDN