How to get the right cable sizing of a circuit from the Ecodial
  • Power Distribution IEC
  • How to get the right cable sizing of a circuit from the Ecodial
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
80
J_Travostino
Sisko J_Travostino Sisko
70
Posted: ‎2020-11-18 03:12 AM . Last Modified: ‎2024-11-22 04:25 AM
2908
Can you please help me to understand how do I optimize cable sizing?
  • Power Distribution Software
Genghiz
Captain
Posted: ‎2020-11-18 11:37 PM . Last Modified: ‎2020-11-18 11:54 PM
1
2899
Thanks for your interest in Ecodial.
The optimum sizing of conductors (cable) for a circuit can be explained by constructing a Simple Network with the "HVLV transformer as a source" and connected to a LV Switchboard. The same Switchboard is also connected a 'Passive load circuit."
 [the above image shows the Simple Network, as explained above]
INPUTS:
At the 'Passive load' circuit, the LOAD and CABLE component characteristics should be provided as the "INPUT properties" to the application. These inputs are considered for sizing the 'conductors (cable) of the circuit.'
LOAD CABLE
OUTPUTS:
Once after calculating the network, the output of the calculations (solution) can be seen at the 'Details' section of the application, and also on the single line diagram of the network.
"Solutions" view will help us to see the sizing results on the SLD single line diagram.  After selecting the circuit component on the SLD, the "Properties" sections will also helps us to see the solutions. After selecting the circuit component on the SLD, the "Details" sections will also helps us to see the solutions.
Output_Properties_SLD.png Output_Properties.png Output_Properties_Details.png
Genghiz
Captain
1
2900
INPUTS:
LOAD CABLE
OUTPUTS:
Genghiz
Captain
Posted: ‎2020-11-22 09:32 PM . Last Modified: ‎2025-08-12 05:21 AM
In response to Genghiz
Here is also an example to see the calculation of conductor sizing for the given inputs.
This article explains the conductor sizing based on the 'Theoretical algorithm' suggested by the IEC 60364-5-52 standard. I hope, this should add further value/answer to your query.