An example for 'determining the smallest allowable cross-sectional area of circuit conductors.'

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • An example for 'determining the smallest allowable cross-sectional area of circuit conductors.'
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
80
J_Travostino
Sisko J_Travostino Sisko
70
View All

Recommended Forums

  • Comunidade de Soluções Elétricas

  • Expert on Demand for Standards & Regulations

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Start a Topic
Solved
Genghiz
Captain Genghiz Captain
Captain

Posted: ‎2020-11-09 11:59 PM . Last Modified: ‎2024-11-22 04:25 AM

1 Like
1
3482
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-09 11:59 PM . Last Modified: ‎2024-11-22 04:25 AM

An example for 'determining the smallest allowable cross-sectional area of circuit conductors.'

From the available inputs;

let us see how to determine the 'smallest allowable cross sectional area' of the circuit conductors.

 

Available inputs;

 

Load Current

200 A

THDi

48 %

Conductor Insulation*

XLPE

Conductor Type

Multi-Core Cable

Conductor Material*

Copper

Installation

Directly in Ground

Soil Resistivity*

2 Km/w

Soil Temperature*

40*C

 

*Some of the inputs are assumed to provide in this example; and they were neither received from the user, nor from the environment.

 

 

Procedure:

 

  • Determinant conductor : Neutral

          As the THDi is > 33 % (that is THDI = 48 %). So, the Size-determining" live conductor is Neutral

 

  • Neutral Current               :  3 × 0.48 × 200 = 288 A

 

  • Correction factor K3       : The factor based on the overload protection device.

           This circuit is assumed to be protected by the circuit-breaker.

           So that the K3 =1.0

 

  • F1 Temperature              : Table B.52.15

          For 40°C and with the insulation XLPE. F1 = 0.85

 

  • Installation method       : 72                                                                                                           (Sheathed single-core or multi-core cables direct in the ground - without added mechanical protection) Reference method          : D2

                                          

  • F2 Group                          : Table B.52.18

          There is no additional touching circuits i.e. total no. of circuits is 1

          F2group = 1.00

 

  • Correction factor F3       : Table (E.52.1)

          THDI >45 % = THDI = 48 %  à f3NeutralTHDI = 1.00

 

  • F3RSoil                              : Table B.52.16

           Installation method = in Ground -> Rth = 2.0 K.m/w

           f3RthSoil = 1.12  

    

  • K user = 1.0

 

Correction factor f

f = 0.85 × 1.00 × 1.00 × 1.05 × 1.00 = 0.952

The overall correction factor is determined by multiplying all 'the available correction factors."

 

 

Theoretical Iz’                 = (K3 x IB) / (F x N live) = (1.0 x 288) / (0.952 x1) = 302.52 A = 303 A

The conductor selection is done from the given Table B.52.5 Column 8 

185 mm2 will be able to carry 324 Amps

240 mm2 will be able to carry 375 Amps

Considering the +5% of tolerance, It would be recommended to consider the size as 185 mm²

 

K3(Correction Factor based on Protection Device)

1

F1(Correction Factor based on Temperature)

0.85

F2(Correction Factor based on Group of conductors)

1

F3(Correction Factor based on THDi)

1

F3(Correction Factor based on Soil Resistivity)

1.05

K user(Correction Factor defined by the user)

1

 

 

Iz’(A) Theoretical

303 A

Iz (A) considered from the table

324 A

Theoretical cross sectional area  Ph (mm²)

1 x 185   mm²

Theoretical cross sectional area Neutral (mm²)

1 x 185   mm²

Theoretical cross sectional area PE (mm²)

1 x 95   mm²

 

 

Labels
  • Labels:
  • Power Distribution Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
dkpElect
Crewman dkpElect
Crewman

Posted: ‎2021-06-26 05:32 AM

1 Like
0
3225
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:32 AM

That's really informative answer. 

Thanks.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
dkpElect
Crewman dkpElect
Crewman

Posted: ‎2021-06-26 05:32 AM

1 Like
0
3226
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:32 AM

That's really informative answer. 

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore