Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-04-12 08:27 AM . Last Modified: 2024-11-22 04:25 AM
1) In a practical scenario, two UPS units (mains) in parallel redundant configuration, are to be fed from two separate sources. By pass of each units are to be from their respective mains itself. However I could not find a way forward to achieve such a criteria in ECODIAL. Kindly advise.
2) I tried to use the design software with 140 symbols but the program was found to be closing un expectedly. As I read through the forums I noticed that the system would work fine with maximum 75 symbols in one project. Hence pls advise how to inter-connect two different projects to solve this as recommended earlier in the forum.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-04-17 04:42 AM . Last Modified: 2023-04-26 02:11 AM
Hai Pradeep,
Thanks for contacting us. we have worked out your queries. please find the solution and attached files.
For query no : 1
We added the 2 UPS in parallel configuration and its fed from two different separate sources. hence, parallel operation of 2 UPS criteria is achieved.
For query no : 2
We have added more than 150 symbols and we can more than this. In this situation application not closed automatically.
We have uploaded the .eac file for both the queries. kindly find the attachments for your reference.
Thanks & Regards
Saravanakumar.L
Ecodial expert support.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-04-17 04:42 AM . Last Modified: 2023-04-26 02:11 AM
Hai Pradeep,
Thanks for contacting us. we have worked out your queries. please find the solution and attached files.
For query no : 1
We added the 2 UPS in parallel configuration and its fed from two different separate sources. hence, parallel operation of 2 UPS criteria is achieved.
For query no : 2
We have added more than 150 symbols and we can more than this. In this situation application not closed automatically.
We have uploaded the .eac file for both the queries. kindly find the attachments for your reference.
Thanks & Regards
Saravanakumar.L
Ecodial expert support.