How to compare NSX and Square D Q0 Trip Curves

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • How to compare NSX and Square D Q0 Trip Curves
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
71
J_Travostino
Sisko J_Travostino Sisko
70
S-W
Commander S-W Commander
66
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Solved
Korkmaz
Crewman Korkmaz
Crewman

Posted: ‎2024-07-01 04:22 AM

0 Likes
9
1099
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-01 04:22 AM

How to compare NSX and Square D Q0 Trip Curves

In our project, we will use NSX MCCB and Square D QO MCB. We can compare and see their curves in ETAP, but some of the CB instantaneous short circuit curves intersect. We generally use energy selectivity in such cases, but Square D is used in the USA while NSX MCCB is used in Europe. Therefore, we couldn't find any table or information about the energy selectivity of these circuit breakers. How can we find or compare information about these circuit breakers?

Thank you in advance for your help and guidance.

Labels
  • Labels:
  • Energy management
  • Medium Voltage
  • Power Availability
  • Power Grid
  • Safety - Electrical Fire Prevention
  • Safety - People Safety
  • Success story
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Gregoire_Brun
Commander Gregoire_Brun Commander
Commander

Posted: ‎2024-07-03 01:35 AM

1 Like
0
1018
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-03 01:35 AM

Hi @Korkmaz I double check on my side with some other expert in Usa 

 

Maybe you can ask the question on this topic

Ecodial Presentation - Schneider Electric Community

 

Gregoire Brun
Breaker Product Expert

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Yarom
Lieutenant JG Yarom Lieutenant JG
Lieutenant JG

Posted: ‎2024-07-04 01:06 PM

4 Likes
2
971
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-04 01:06 PM

I used to support locally in North America the Square D UL protection devices. Then I moved to where IEC is the standard.

 

Let's understand first a bit of the background.  You cannot really compare such curves as each type (QO/U, NSX, PowerPact and so on) are tested specific to the standard for which they are intended. The standards of how trip curves work in UL do not necessarily coincide with those of the IEC. Although PowerPact are similar, they are not necessarily interchangeable. There are some NSX breaker that have UL and IEC ratings.

 

What this gives is so that you can install in either place (where UL or IEC is accepted by law), but according to regulations of that standard for which your panel must adhere.

 

For example, in the U.S. and Canada they follow UL 489, 508, 1077. Each has a specific application.

489 = Branch Circuit
508 = is a combination for the panel including Feeder circuit and Branch circuits at minimum.
1077 = Supplementary protection for control circuits.

 

Feeder Circtuit
Incoming to the panel and feeding all the branches, you must install a 489 breaker or UL 98 fuse or non-fuse (separate fuse holder) disconnect switch or UL 248 combination fused disconnect switches. to feed anything below.

 

Branch Circuit

If you have a control transformer dropping 480/600 (2 phases) to 230 or less single phase to a group of control devices, you must have the 489 type breaker at the primary and can use the 1077 type miniature circuit breaker at the secondary, for any of the control side wire protection.

 

This is a mere basic example of the complexities of breakers in UL panels. These standards are designed and tested. The IEC does not follow this method of protection. IEC follows as EcoDial shows and is programmed, to calculate cascading, selectivity, cables and other electrical properties.

 

UL has another property required -> SCCR (Short Circuit Current Rating)

IEC does not consider SCCR. This again, from the graphs of IEC breakers, tells us the energy and from there we calculate cables and busbars (again EcoDial).

 

To understand more about this UL information, please download the Schneider Electric Technical guide:

 

https://www.se.com/us/en/download/document/CPTG005_EN/ 

 

QO trip curves can be found in the catalog:

 

https://www.se.com/us/en/download/document/0730CT9801/

 

Any other trip curve can be found in their respective catalog.

 

For NSX breakers, use the Country website following IEC standards.

 

For PowerPact breakers, use the U.S. or Canadian website.

 

Conclusion:

 

Since UL and IEC are not equivalent standards, but alternatives, we cannot compare the two as they are not tested following the same standards. Each type has a curve generated according to the standard.

 

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
Gregoire_Brun
Commander Gregoire_Brun Commander
Commander

Posted: ‎2024-07-02 12:59 AM

1 Like
0
1070
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-02 12:59 AM

Hello @Korkmaz 

 

Your application looks strange for me because to mix a product certified Ul489 and another certified IEC 60-947-2

What can be the standard for your equipment on this case?

Maybe if you need UL products, it should be better to use Powerpact B H J L to replace the compact NSX  

Gregoire Brun
Breaker Product Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

Korkmaz
Crewman Korkmaz
Crewman

Posted: ‎2024-07-02 04:47 AM

0 Likes
0
1056
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-02 04:47 AM

Maybe it better , but i want to know that how can i compare two circuit breaker according to energy selectivity without tables ?

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Gregoire_Brun
Commander Gregoire_Brun Commander
Commander

Posted: ‎2024-07-02 07:48 AM

0 Likes
0
1044
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-02 07:48 AM

please check if this tool can help you

EcoStruxure Power Design – Ecodial | Schneider Electric TR (se.com)

Gregoire Brun
Breaker Product Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

Korkmaz
Crewman Korkmaz
Crewman

Posted: ‎2024-07-03 12:31 AM

0 Likes
0
1029
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-03 12:31 AM

Hello @Gregoire_Brun 

I appreciate your support and responses , i checked and installed Ecodial but couldn't find Square D type circuit breakers in Ecodial only find NSX and other type of europe side circuit breakers

Reply

Link copied. Please paste this link to share this article on your social media post.

Gregoire_Brun
Commander Gregoire_Brun Commander
Commander

Posted: ‎2024-07-03 01:35 AM

1 Like
0
1019
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-03 01:35 AM

Hi @Korkmaz I double check on my side with some other expert in Usa 

 

Maybe you can ask the question on this topic

Ecodial Presentation - Schneider Electric Community

 

Gregoire Brun
Breaker Product Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

Yarom
Lieutenant JG Yarom Lieutenant JG
Lieutenant JG

Posted: ‎2024-07-04 01:06 PM

4 Likes
2
972
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-04 01:06 PM

I used to support locally in North America the Square D UL protection devices. Then I moved to where IEC is the standard.

 

Let's understand first a bit of the background.  You cannot really compare such curves as each type (QO/U, NSX, PowerPact and so on) are tested specific to the standard for which they are intended. The standards of how trip curves work in UL do not necessarily coincide with those of the IEC. Although PowerPact are similar, they are not necessarily interchangeable. There are some NSX breaker that have UL and IEC ratings.

 

What this gives is so that you can install in either place (where UL or IEC is accepted by law), but according to regulations of that standard for which your panel must adhere.

 

For example, in the U.S. and Canada they follow UL 489, 508, 1077. Each has a specific application.

489 = Branch Circuit
508 = is a combination for the panel including Feeder circuit and Branch circuits at minimum.
1077 = Supplementary protection for control circuits.

 

Feeder Circtuit
Incoming to the panel and feeding all the branches, you must install a 489 breaker or UL 98 fuse or non-fuse (separate fuse holder) disconnect switch or UL 248 combination fused disconnect switches. to feed anything below.

 

Branch Circuit

If you have a control transformer dropping 480/600 (2 phases) to 230 or less single phase to a group of control devices, you must have the 489 type breaker at the primary and can use the 1077 type miniature circuit breaker at the secondary, for any of the control side wire protection.

 

This is a mere basic example of the complexities of breakers in UL panels. These standards are designed and tested. The IEC does not follow this method of protection. IEC follows as EcoDial shows and is programmed, to calculate cascading, selectivity, cables and other electrical properties.

 

UL has another property required -> SCCR (Short Circuit Current Rating)

IEC does not consider SCCR. This again, from the graphs of IEC breakers, tells us the energy and from there we calculate cables and busbars (again EcoDial).

 

To understand more about this UL information, please download the Schneider Electric Technical guide:

 

https://www.se.com/us/en/download/document/CPTG005_EN/ 

 

QO trip curves can be found in the catalog:

 

https://www.se.com/us/en/download/document/0730CT9801/

 

Any other trip curve can be found in their respective catalog.

 

For NSX breakers, use the Country website following IEC standards.

 

For PowerPact breakers, use the U.S. or Canadian website.

 

Conclusion:

 

Since UL and IEC are not equivalent standards, but alternatives, we cannot compare the two as they are not tested following the same standards. Each type has a curve generated according to the standard.

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

zolos9479
zolos9479
Cadet

Posted: ‎2024-08-12 01:32 PM

In response to Yarom
0 Likes
1
792
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-12 01:32 PM

I would like to clarify the following question with you:
According to the Control Panel Technical Guide, can I use the Multi 9 M9F42350 https://eref.se.com/us/en/scope/product/M9F42350 as Feeder circuits (Incoming protective devices)? It complies with UL489, but its rated operational voltage is max.440V according to the datasheet. How then can I use it for three phases 480Y /277V. Also, what does "..." mean in the table on page 20?
Or on the input option only https://www.se.com/us/en/product/EDB34050/mini-circuit-breaker-eframe-50a-3-pole-480y-277vac-25ka-ma... or https://www.se.com/us/en/product/BDP36050/circuit-breaker-powerpact-b-50a-3-pole-600y-347vac-14ka-lu...
Thank you for your answer

Reply

Link copied. Please paste this link to share this article on your social media post.

Gregoire_Brun
Commander Gregoire_Brun Commander
Commander

Posted: ‎2024-08-14 12:33 AM

1 Like
0
787
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-14 12:33 AM

hello @zolos9479 

I wouldn't recommend tuo use the multi9 product for your needed , an dI recommend to use the powerpact B for this application

 

Gregoire Brun
Breaker Product Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

Yarom
Lieutenant JG Yarom Lieutenant JG
Lieutenant JG

Posted: ‎2024-08-15 05:30 AM

In response to zolos9479
0 Likes
0
764
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-15 05:30 AM

Let's clear up a little bit.

 

You looked at the M9F42350. The Multi9 series is designed for OEM usage, and were give multiple standards.  We see the UL489 as well as IEC947.

You have to be careful when reading datasheets. When you open the datasheet that you referred:

https://eref.se.com/us/en/scope/product/M9F42350, look at the table of standards for the breaking capacity values.

6 kA Icu 440 V AC EN/IEC 60947-2
10 kA Icu 415 V AC EN/IEC 60947-2
20 kA Icu 240 V AC EN/IEC 60947-2
6 kA Icu 440 V AC GB 14048.2
10 kA Icu 415 V AC GB 14048.2
20 kA Icu 240 V AC GB 14048.2
10 kA AIR 240 V AC UL 489
10 kA AIR 240 V AC CSA C22.2 No 5

440V is rated for Countries following the IEC (European) and GB has it's own. These countries run 400V 3phase +/- 10% allowance. Hence, the 440V value.

 

Nowhere does it mention UL489 for those voltage ratings. For UL489, you can use it on up to 240V. So you can use it as a feeder to a branch that has an oven rated 208V ph-ph for example.

 

For more details on this series of circuit breaker, you can download the catalog:

 

https://www.se.com/us/en/download/document/LVCATM9OEM_EN/

 

Regarding the question of 480/277, the EDB breaker is an original Square D brand breaker, designed for the U.S. market. The use standard industrial 3 phase voltage is 480V phase to phase, which gives 277 phase to neutral. So for any application or equipment using those standard voltages (277V Ph-N could be lighting, 480V Ph-Ph could be a 3 phase motor), you would use this type of breaker for the branch circuit.  It is tested and certrified according the UL and CSA standards.

 

In Canada, the standard industrial voltage is 600V Ph-Ph or 347V Ph-N. Here, the EDB will not satisfy equipment connecting to this electrical network.

The PowerPact B breaker does satisfy the conditions to work up to 600V Ph-Ph / 347V Ph-N.

 

Again, all these have to do with the requirements of the regional standard. It is not a question about take something cheaper that seems close enough or why is it 40V too low for what is needed. Do not forget that 10% +/- has to be taken into account. 440V is the maximum.  And to get back to the original question, because of the difference in standards, thereby, different testing procedures and requirements, they cannot be necessarily compared.

 

As Gregoir Brun mentioned, for your application, it is best to stick with PowerPact B.

 

Best regards

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of