Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-04-29 01:25 AM
If Schneider Electric ACB and MCCB (400A and above) can be used without Micrologic tripping unit? the tripping will be activated only by external relay. If yes, kindly explain how it works.
thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-08-09 05:05 AM
hello @HH1
it's possible to use some ACB without trip unit where you can use an external relay equivalent like for medium voltage network. On this case, order to open will be gived to the breaker by a coil (MX).
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-08-09 05:05 AM
hello @HH1
it's possible to use some ACB without trip unit where you can use an external relay equivalent like for medium voltage network. On this case, order to open will be gived to the breaker by a coil (MX).