Fusegear vs circuit breaker , what do you think ?

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • Fusegear vs circuit breaker , what do you think ?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
80
J_Travostino
Sisko J_Travostino Sisko
70
View All

Recommended Forums

  • Comunidade de Soluções Elétricas

  • Expert on Demand for Standards & Regulations

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Start a Topic
Solved
Fabien_Mastrot
Fabien_Mastrot Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2022-03-18 09:02 AM

4 Likes
3
3047
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-18 09:02 AM

Fusegear vs circuit breaker , what do you think ?

Hi,

let's re open a old historical debate between Circuit breaker vs Fusegear .

 

There are 2 different ways to protect people and electrical installation. 

 

How do use this different types of devices (Fusegear and/or Circuit breaker) in your application and switchboard ? 

 

Share your experience and vision .

 

Thanks

Fabien

Fabien Mastrot
EcoXpert global badge owner
Labels
  • Labels:
  • Products
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2022-03-23 12:42 AM

1 Like
1
2962
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-23 12:42 AM

Hello @Fabien_Mastrot 

 

Here are my thoughts on this very interesting question.

 

Obviously, they both offer overcurrent protection of electric power distribution systems. Dimensioning is also not a choice criterion: both fuses and circuit breakers are available in a diversity of sizes, ratings,…

 

The main difference between fuses and circuit breakers is the fact that the fuse is “cut off” by overcurrent while a circuit breaker opens the circuit without damage to itself.

 

However, I think several other factors/features must be considered:

  > Disconnecting function: if using fuse, you should add a disconnecting device (like switches) while circuit breakers integrate it.

  >Ground Fault Protection function: fuses cannot provide ground fault protection or earth leakage protection while circuit breakers can (considering you’ve selected the right one)

 

In addition, circuit breakers can embed (without additional devices needed):

 > Adjustable tripping parameters if circuit breaker is equipped (especially electronic with trip unit)

 > Control and Monitoring features

 

Finally, I guess it depends, also and mainly, on local regulations, cost optimization and of course historical habits…

 

 

 

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

RHH
Commander | EcoXpert Master RHH Commander | EcoXpert Master
Commander | EcoXpert Master

Posted: ‎2022-03-23 01:00 AM . Last Modified: ‎2022-03-23 01:04 AM

In response to Anonymous user
2 Likes
0
2955
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-23 01:00 AM . Last Modified: ‎2022-03-23 01:04 AM

Very true!


As part of a panel builder it mainly rely's on what the customer asks.
But sometimes we advice on the use of fuses instead of using circuit-breakers.

This is mostly the case if there is selectivity involved which the breakers chosen for the circuit cannot

or are not fully selective behind eachother, while this is still a wish and demand from the customer.

In any case, we try to use circuit breakers more and more often as they usually just break the circuit instead of cutting itself out like a fuse does (as @Anonymous user already mentioned). Less hassle for the people to get the power back without having to have knowledge of fuses etc.

P.s. fuses do have high kA capacity, especially for 63A and below. This is a big win on the ground of fuses where circuit breakers are getting alot more expensive and bigger to reach the same kA capacity. (Try comparing a Neozed 4P 63A (Din-modulair) to a NSX(m) and you see what I mean)

 

 


Kind regards,

Rick

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2022-03-23 12:42 AM

1 Like
1
2963
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-23 12:42 AM

Hello @Fabien_Mastrot 

 

Here are my thoughts on this very interesting question.

 

Obviously, they both offer overcurrent protection of electric power distribution systems. Dimensioning is also not a choice criterion: both fuses and circuit breakers are available in a diversity of sizes, ratings,…

 

The main difference between fuses and circuit breakers is the fact that the fuse is “cut off” by overcurrent while a circuit breaker opens the circuit without damage to itself.

 

However, I think several other factors/features must be considered:

  > Disconnecting function: if using fuse, you should add a disconnecting device (like switches) while circuit breakers integrate it.

  >Ground Fault Protection function: fuses cannot provide ground fault protection or earth leakage protection while circuit breakers can (considering you’ve selected the right one)

 

In addition, circuit breakers can embed (without additional devices needed):

 > Adjustable tripping parameters if circuit breaker is equipped (especially electronic with trip unit)

 > Control and Monitoring features

 

Finally, I guess it depends, also and mainly, on local regulations, cost optimization and of course historical habits…

 

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

RHH
Commander | EcoXpert Master RHH Commander | EcoXpert Master
Commander | EcoXpert Master

Posted: ‎2022-03-23 01:00 AM . Last Modified: ‎2022-03-23 01:04 AM

In response to Anonymous user
2 Likes
0
2956
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-23 01:00 AM . Last Modified: ‎2022-03-23 01:04 AM

Very true!


As part of a panel builder it mainly rely's on what the customer asks.
But sometimes we advice on the use of fuses instead of using circuit-breakers.

This is mostly the case if there is selectivity involved which the breakers chosen for the circuit cannot

or are not fully selective behind eachother, while this is still a wish and demand from the customer.

In any case, we try to use circuit breakers more and more often as they usually just break the circuit instead of cutting itself out like a fuse does (as @Anonymous user already mentioned). Less hassle for the people to get the power back without having to have knowledge of fuses etc.

P.s. fuses do have high kA capacity, especially for 63A and below. This is a big win on the ground of fuses where circuit breakers are getting alot more expensive and bigger to reach the same kA capacity. (Try comparing a Neozed 4P 63A (Din-modulair) to a NSX(m) and you see what I mean)

 

 


Kind regards,

Rick
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

jameslandry
Crewman jameslandry
Crewman

Posted: ‎2023-12-03 08:20 PM

1 Like
0
1994
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-12-03 08:20 PM

I think the best option depends on the type and size of the application and switchboard, as well as the personal preference and budget. Some experts suggest that a combination of both fusegear and circuit breaker may be the optimal solution, as it can provide the benefits of both devices and compensate for their drawbacks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore