How to limit Short circuit by cascading
  • Power Distribution IEC
  • How to limit Short circuit by cascading
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
80
J_Travostino
Sisko J_Travostino Sisko
70
hareeshks
hareeshks
Cadet
Posted: ‎2023-10-31 07:10 AM
1346
I have a 400V, 65kA LV switchgear. I would like to connect a feeder from this LV switchgear to a DB with 25kA rating. In order to avoid the transformer to limit the short circuit, is it possible to use the cascading (current limiting type) breakers in both upstream and downstream? Any selection tools based on short circuit limitations?
  • How to
geir_eas_no_bfo
Lt. Commander geir_eas_no_bfo
Lt. Commander
Posted: ‎2023-11-03 04:35 AM
1
1337
yes you can.
check out these tools: https://ect.se.com/cbt/app/index.html#/Dashboard
BR
GIA
geir_eas_no_bfo
Lt. Commander
Posted: ‎2023-11-03 06:52 AM
Yes.
You will find this in Complementary Technical information:
BR
GIA
geir_eas_no_bfo
Lt. Commander
1
1338
yes you can.
BR
GIA
hareeshks
hareeshks
Cadet
Posted: ‎2023-11-03 05:13 AM
In response to geir_eas_no_bfo
Thank you. Is there any impact on breaker selectivity in this case (current limiting). Will upstream breaker open for downstream fault?
geir_eas_no_bfo
Lt. Commander
Yes.
BR
GIA