Ecodial transformer secondary connection

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • Ecodial transformer secondary connection
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
71
J_Travostino
Sisko J_Travostino Sisko
70
S-W
Commander S-W Commander
66
View All
Related Products
product field
Schneider Electric
Trihal

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Solved
KrunoslavSever
Ensign KrunoslavSever Ensign
Ensign

Posted: ‎2025-04-30 04:36 AM

0 Likes
2
351
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-30 04:36 AM

Ecodial transformer secondary connection

Hello,

I have a customer with existing installation of two switchboards directly connected to secondary of trihal transfomer. Network with one connected switchboard you can find in attachment - drafted by the customer. So, overall network consist of two 630 amp switchboards directly connected to secondary of trihal via 4*150 mm2 aluminum cables. Is this configuration possible to design in ecodial?

 

Thank you,

Best regards,

K

Attachments
test.eac
Labels
  • Labels:
  • How to
  • Knowledge
  • Medium Voltage
  • Power Grid
  • Tags:
  • ecodial
  • english
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Darini
Crewman Darini Crewman
Crewman

Posted: ‎2025-05-20 03:34 AM

0 Likes
0
250
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-20 03:34 AM

Hello K,

Ecodial typically models a single main outgoing feeder from a transformer. Directly connecting two main switchboards from the same transformer secondary is not a standard modeling approach in Ecodial, and it doesn’t natively support multiple direct connections from a single transformer output.

 

   Workaround in Ecodial:

 

You can model this setup by:

 

  Creating a main LV switchboard (e.g., MSB) connected to the transformer.

 

  Then, from the MSB, you can draw two outgoing feeders (each with their own protection) going to SB1 and SB2.

 

  •  This may not reflect the exact physical layout, but it helps in performing load flow, short-circuit, and protection coordination calculations accurately.

 

Thank you for sharing the .eac file and the installation details.
Key Issues Identified in project:
1. Voltage Drop Exceeded:
• The error message for WD0 “The cable is not compatible . The voltage drop exceeds the permissible maximum” indicates that the 4×150 mm² Al cable over 145 m results in a voltage drop that exceeds the recommended 3% limit for feeder circuits as per IEC 60364-5-52, which may affect performance, especially for voltage-sensitive equipment.


2. Circuit Breaker Sizing – MTZ06H1:


• The current CB is shown as undersized in Ecodial.
• Upon unlocking the settings, Ecodial recommends upgrading the cable to 3×300 mm² Al (+PEN) and using a NS1600 circuit breaker instead of the current MTZ06H1.
• This ensures both thermal compatibility and acceptable voltage drop across the feeder.
⸝
Recommended Actions:
1. Upgrade Cable Sizing:
• For each 630 A feeder, use either:
• One run of 4×240 mm² Al cable, or
• Two parallel runs of 4×150 mm² Al cable.
• For the source feeder, consider upgrading to 3×300 mm² Al + PEN cable as suggested.
2. Upgrade Circuit Breaker:
• Replace MTZ06H1 with NS1600, or another appropriate breaker, as per the cable capacity and expected load.
3. Compliance Confirmation:
• These updates will ensure compliance with voltage drop limits and thermal sizing in Ecodial and align with IEC standards for LV design.

Please let me know if you need further assistance.

Regards, 

Darini H.D

CPS expert support

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Manon_Chaboud
Commander Manon_Chaboud Commander
Commander

Posted: ‎2025-04-30 07:34 AM

1 Like
0
341
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-30 07:34 AM

Hello @KrunoslavSever, thank you for your post!

@Saravanakumar.L, can you please advise @KrunoslavSever? Thank you in advance 🙂

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Darini
Crewman Darini Crewman
Crewman

Posted: ‎2025-05-20 03:34 AM

0 Likes
0
251
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-20 03:34 AM

Hello K,

Ecodial typically models a single main outgoing feeder from a transformer. Directly connecting two main switchboards from the same transformer secondary is not a standard modeling approach in Ecodial, and it doesn’t natively support multiple direct connections from a single transformer output.

 

   Workaround in Ecodial:

 

You can model this setup by:

 

  Creating a main LV switchboard (e.g., MSB) connected to the transformer.

 

  Then, from the MSB, you can draw two outgoing feeders (each with their own protection) going to SB1 and SB2.

 

  •  This may not reflect the exact physical layout, but it helps in performing load flow, short-circuit, and protection coordination calculations accurately.

 

Thank you for sharing the .eac file and the installation details.
Key Issues Identified in project:
1. Voltage Drop Exceeded:
• The error message for WD0 “The cable is not compatible . The voltage drop exceeds the permissible maximum” indicates that the 4×150 mm² Al cable over 145 m results in a voltage drop that exceeds the recommended 3% limit for feeder circuits as per IEC 60364-5-52, which may affect performance, especially for voltage-sensitive equipment.


2. Circuit Breaker Sizing – MTZ06H1:


• The current CB is shown as undersized in Ecodial.
• Upon unlocking the settings, Ecodial recommends upgrading the cable to 3×300 mm² Al (+PEN) and using a NS1600 circuit breaker instead of the current MTZ06H1.
• This ensures both thermal compatibility and acceptable voltage drop across the feeder.
⸝
Recommended Actions:
1. Upgrade Cable Sizing:
• For each 630 A feeder, use either:
• One run of 4×240 mm² Al cable, or
• Two parallel runs of 4×150 mm² Al cable.
• For the source feeder, consider upgrading to 3×300 mm² Al + PEN cable as suggested.
2. Upgrade Circuit Breaker:
• Replace MTZ06H1 with NS1600, or another appropriate breaker, as per the cable capacity and expected load.
3. Compliance Confirmation:
• These updates will ensure compliance with voltage drop limits and thermal sizing in Ecodial and align with IEC standards for LV design.

Please let me know if you need further assistance.

Regards, 

Darini H.D

CPS expert support

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Š 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of