Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, letâs discuss how digital and software are transforming your business and your day-to-day work.
Link copied. Please paste this link to share this article on your social media post.
Posted: â2025-04-30 04:36 AM
Hello,
I have a customer with existing installation of two switchboards directly connected to secondary of trihal transfomer. Network with one connected switchboard you can find in attachment - drafted by the customer. So, overall network consist of two 630 amp switchboards directly connected to secondary of trihal via 4*150 mm2 aluminum cables. Is this configuration possible to design in ecodial?
Thank you,
Best regards,
K
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: â2025-05-20 03:34 AM
Hello K,
Ecodial typically models a single main outgoing feeder from a transformer. Directly connecting two main switchboards from the same transformer secondary is not a standard modeling approach in Ecodial, and it doesnât natively support multiple direct connections from a single transformer output.
âââWorkaround in Ecodial:
You can model this setup by:
ââCreating a main LV switchboard (e.g., MSB) connected to the transformer.
ââThen, from the MSB, you can draw two outgoing feeders (each with their own protection) going to SB1 and SB2.
âââ˘ââThis may not reflect the exact physical layout, but it helps in performing load flow, short-circuit, and protection coordination calculations accurately.
Thank you for sharing the .eac file and the installation details.
Key Issues Identified in project:
1. Voltage Drop Exceeded:
⢠The error message for WD0 âThe cable is not compatible . The voltage drop exceeds the permissible maximumâ indicates that the 4Ă150 mm² Al cable over 145 m results in a voltage drop that exceeds the recommended 3% limit for feeder circuits as per IEC 60364-5-52, which may affect performance, especially for voltage-sensitive equipment.
2. Circuit Breaker Sizing â MTZ06H1:
⢠The current CB is shown as undersized in Ecodial.
⢠Upon unlocking the settings, Ecodial recommends upgrading the cable to 3Ă300 mm² Al (+PEN) and using a NS1600 circuit breaker instead of the current MTZ06H1.
⢠This ensures both thermal compatibility and acceptable voltage drop across the feeder.
⸝
Recommended Actions:
1. Upgrade Cable Sizing:
⢠For each 630 A feeder, use either:
⢠One run of 4Ă240 mm² Al cable, or
⢠Two parallel runs of 4Ă150 mm² Al cable.
⢠For the source feeder, consider upgrading to 3Ă300 mm² Al + PEN cable as suggested.
2. Upgrade Circuit Breaker:
⢠Replace MTZ06H1 with NS1600, or another appropriate breaker, as per the cable capacity and expected load.
3. Compliance Confirmation:
⢠These updates will ensure compliance with voltage drop limits and thermal sizing in Ecodial and align with IEC standards for LV design.
Please let me know if you need further assistance.
Regards,
Darini H.D
CPS expert support
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: â2025-04-30 07:34 AM
Hello @KrunoslavSever, thank you for your post!
@Saravanakumar.L, can you please advise @KrunoslavSever? Thank you in advance đ
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: â2025-05-20 03:34 AM
Hello K,
Ecodial typically models a single main outgoing feeder from a transformer. Directly connecting two main switchboards from the same transformer secondary is not a standard modeling approach in Ecodial, and it doesnât natively support multiple direct connections from a single transformer output.
âââWorkaround in Ecodial:
You can model this setup by:
ââCreating a main LV switchboard (e.g., MSB) connected to the transformer.
ââThen, from the MSB, you can draw two outgoing feeders (each with their own protection) going to SB1 and SB2.
âââ˘ââThis may not reflect the exact physical layout, but it helps in performing load flow, short-circuit, and protection coordination calculations accurately.
Thank you for sharing the .eac file and the installation details.
Key Issues Identified in project:
1. Voltage Drop Exceeded:
⢠The error message for WD0 âThe cable is not compatible . The voltage drop exceeds the permissible maximumâ indicates that the 4Ă150 mm² Al cable over 145 m results in a voltage drop that exceeds the recommended 3% limit for feeder circuits as per IEC 60364-5-52, which may affect performance, especially for voltage-sensitive equipment.
2. Circuit Breaker Sizing â MTZ06H1:
⢠The current CB is shown as undersized in Ecodial.
⢠Upon unlocking the settings, Ecodial recommends upgrading the cable to 3Ă300 mm² Al (+PEN) and using a NS1600 circuit breaker instead of the current MTZ06H1.
⢠This ensures both thermal compatibility and acceptable voltage drop across the feeder.
⸝
Recommended Actions:
1. Upgrade Cable Sizing:
⢠For each 630 A feeder, use either:
⢠One run of 4Ă240 mm² Al cable, or
⢠Two parallel runs of 4Ă150 mm² Al cable.
⢠For the source feeder, consider upgrading to 3Ă300 mm² Al + PEN cable as suggested.
2. Upgrade Circuit Breaker:
⢠Replace MTZ06H1 with NS1600, or another appropriate breaker, as per the cable capacity and expected load.
3. Compliance Confirmation:
⢠These updates will ensure compliance with voltage drop limits and thermal sizing in Ecodial and align with IEC standards for LV design.
Please let me know if you need further assistance.
Regards,
Darini H.D
CPS expert support
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of