Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-04-17 01:26 PM . Last Modified: 2025-04-17 01:27 PM
Hi everyone,
I am working in a project that includes the sharing of voltage measurement among 9 SM6 24kV switchgears. They are all standard versions of the DM1-A option and we bought and installed 3 VTs (13.8R3 - 0.12R3 KV) in the incomming switchgear. The client has specifically asked to have voltage and power measurements in all 9 relays (P3U30), but they only have LPVT inputs. We managed to find an adapter (EMS59572) which helped us transform the VTs output into an LPVT signal. The readings were successful and we were able to configure the relay to that signal.
The problem we have now is that we cannot find more of these adapters and we still need 8 more to connect the remaining relays to the voltage signal. We found in the PowerLogic P3 catalogue an LPVT transducer (P7M12025) which apparently allows the connection from 1 LPVT signal to up to 10 P3 relays.
I cannot find any more information regarding this transducer, so I would like to know if anyone here knows how to integrate this device into the system described above, or if anyone has worked with this transducer before so they can explain to me how the signal is shared to all 10 allowed devices.
Thanks for the help!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-22 12:51 AM
Hello Nicolas,
This question is managed by the Protection and Control forums here https://community.se.com/t5/EcoStruxure-Power-Grid/ct-p/power-management
But to answer your specific point I attach an application note that explains how to share LPVT signals. It is written for a P5 relay but is equally applicable to P3
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-22 12:51 AM
Hello Nicolas,
This question is managed by the Protection and Control forums here https://community.se.com/t5/EcoStruxure-Power-Grid/ct-p/power-management
But to answer your specific point I attach an application note that explains how to share LPVT signals. It is written for a P5 relay but is equally applicable to P3
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of