Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

LPTV SIGNAL SHARING TO 9 SM6 24KV SWITCHGEARS USING P3U30 RELAY

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • LPTV SIGNAL SHARING TO 9 SM6 24KV SWITCHGEARS USING P3U30 RELAY
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
77
J_Travostino
Sisko J_Travostino Sisko
70
S-W
Commander S-W Commander
67
View All
Related Products
product field
Schneider Electric
SM6 Switchgear
product field
PowerLogic
PowerLogic P3

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Start a Topic
Solved
nicolasjacome
Ensign nicolasjacome
Ensign

Posted: ‎2025-04-17 01:26 PM . Last Modified: ‎2025-04-17 01:27 PM

0 Likes
2
1300
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-17 01:26 PM . Last Modified: ‎2025-04-17 01:27 PM

LPTV SIGNAL SHARING TO 9 SM6 24KV SWITCHGEARS USING P3U30 RELAY

Hi everyone,

 

I am working in a project that includes the sharing of voltage measurement among 9 SM6 24kV switchgears. They are all standard versions of the DM1-A option and we bought and installed 3 VTs (13.8R3 - 0.12R3 KV) in the incomming switchgear. The client has specifically asked to have voltage and power measurements in all 9 relays (P3U30), but they only have LPVT inputs. We managed to find an adapter (EMS59572) which helped us transform the VTs output into an LPVT signal. The readings were successful and we were able to configure the relay to that signal.

 

The problem we have now is that we cannot find more of these adapters and we still need 8 more to connect the remaining relays to the voltage signal. We found in the PowerLogic P3 catalogue an LPVT transducer (P7M12025) which apparently allows the connection from 1 LPVT signal to up to 10 P3 relays.

 

I cannot find any more information regarding this transducer, so I would like to know if anyone here knows how to integrate this device into the system described above, or if anyone has worked with this transducer before so they can explain to me how the signal is shared to all 10 allowed devices.

 

Thanks for the help!

Labels
  • Labels:
  • Medium Voltage
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Pete_Vivers
Captain Pete_Vivers Captain
Captain

Posted: ‎2025-05-22 12:51 AM

In response to Manon_Chaboud
0 Likes
0
843
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-22 12:51 AM

Hello Nicolas,

This question is managed by the Protection and Control forums here https://community.se.com/t5/EcoStruxure-Power-Grid/ct-p/power-management

But to answer your specific point I attach an application note that explains how to share LPVT signals. It is written for a P5 relay but is equally applicable to P3

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Manon_Chaboud
Commander Manon_Chaboud Commander
Commander

Posted: ‎2025-04-18 12:23 AM

0 Likes
1
1214
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-18 12:23 AM

Hello @nicolasjacome, thank you for your post, we'll come back to you!

Reply

Link copied. Please paste this link to share this article on your social media post.

Pete_Vivers
Captain Pete_Vivers Captain
Captain

Posted: ‎2025-05-22 12:51 AM

In response to Manon_Chaboud
0 Likes
0
844
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-22 12:51 AM

Hello Nicolas,

This question is managed by the Protection and Control forums here https://community.se.com/t5/EcoStruxure-Power-Grid/ct-p/power-management

But to answer your specific point I attach an application note that explains how to share LPVT signals. It is written for a P5 relay but is equally applicable to P3

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore