Ecodial - closed loop network
  • Power Distribution IEC
  • Ecodial - closed loop network
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
80
J_Travostino
Sisko J_Travostino Sisko
70
KrunoslavSever
Ensign KrunoslavSever Ensign
Ensign
Posted: ‎2023-11-30 05:54 AM . Last Modified: ‎2024-11-22 04:25 AM
1407
is there a way to make closed loop calculations in ecodial? I have a specifier that wants to make three busbar trunking lines between switchboards. Any way around it? Will it be available in future?
Thank you,
Best regards
K
  • Power Distribution Software
Genghiz
Captain
Posted: ‎2023-11-30 10:10 PM
Hello
Thanks for your query about ‘EcoStruxure Power Design – Ecodial’
Comments:
The looped networks are not allowed in the Ecodial application. So, if we create a network with the presence of a loop will create an ‘error message.’
Workaround:
As per the given example, there are ‘3 busbar trunking lines’ are connected between 2 switchboards. There is only one line is in a closed condition, and the remaining two are in open condition.
So, the combination of ‘other two operating scenarios’ can be created with ‘one line is closed’ and ‘other two lines are open.’
Operating Scenarios:
The 3 operating scenarios defined, for any ‘one of the lines is closed’ should make this project accepted and calculated by the application.
Thanks & Regards,
Team – Ecodial Expert Support.
Genghiz
Captain
Hello
Comments:
Workaround:
Thanks & Regards,
Genghiz
Captain
Posted: ‎2023-11-30 10:24 PM
As explained above the 3 operating modes of the project is explained as follows.
Operating Mode 1Operating Mode 1
Operating Mode 2Operating Mode 2
Operating Mode 3Operating Mode 3
KrunoslavSever
Ensign
Posted: ‎2023-12-01 01:40 AM
Thank you Genghiz,
I'll propose this method.
Best regards,
K