I am looking for a legend which I can attach to the report for the values that are available in the report as below
Ik3max
Ik2max
Ik1max
Ik2min
Ik1min
Iefmin
Ief2min
Iefmax
  • Power Distribution Software
Genghiz
Captain
Posted: ‎2023-07-28 03:06 AM
Hello Abdul,
Here is the list of legends received from the 'product development team.' If any clarifications needed, kindly please come back.
Code Definition
Iz Load current values(This is calculated along with load current and compensation current due to various derating factors)
Ik3M Possible maximum short circuit current calculation when there is 3 phase fault occurs
Ik2M Possible maximum short circuit current calculation when 2 phase fault occurs
Ik1M Possible maximum short circuit current calculation when single phase to ground/earth fault occurs
Ik2min Possible minimum short circuit current calculation when 2 phase fault occurs
Ik1min Possible minimum short circuit current calculation when single phase to ground/earth fault occurs
Iefmax Possible Maximum short circuit current calculation when earth fault occurs
Ief2min Possible minimum short circuit current calculation when 2  phase to earth fault occurs
∑∆u3p (%) Percentage of "cumulated voltage drop" from upstream for 3 phase circuit
∆U3L (%) Percentage voltage drop for 3 phase circuit
∆UL1L2 (%) Percentage voltage drop between 2 phases .ie, L1 & L2
∆UL2L3 (%) Percentage voltage drop between 2 phases .ie, L2 & L3
∆UL3L1 (%) Percentage voltage drop between 2 phases .ie, L3 & L1
∆UL1N (%) Percentage voltage drop between 1 phases .ie, L1 & N
∆UL2N (%) Percentage voltage drop between 1 phases .ie, L2 & N
∆UL3N (%) Percentage voltage drop between 1 phases .ie, L3 & N
Thanks & Regads,
Team - Ecodial Expert Support
Genghiz
Captain
Hello Abdul,
Code Definition
Thanks & Regads,
Proyectos11
Proyectos11
Cadet
Posted: ‎2023-11-20 08:03 PM
Hola, quisiera saber si puedo modificar este valor de ik3max?