Ecodial 5.3.1. medium voltage cable

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • Ecodial 5.3.1. medium voltage cable
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
71
J_Travostino
Sisko J_Travostino Sisko
70
S-W
Commander S-W Commander
66
View All
Related Products
product field
Schneider Electric
EcoStruxure™ Power Design – Ecodial

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Solved
KrunoslavSever
Ensign KrunoslavSever Ensign
Ensign

Posted: ‎2025-03-03 08:14 AM

0 Likes
6
387
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-03 08:14 AM

Ecodial 5.3.1. medium voltage cable

Hello,

 

is there a way to see options for medium voltage cable ? Client is expecting a much lower proposed solution but keeps getting high cross section. As per cable manufacturer, 70 mm2 should be enough but ecoidal keeps proposing 185 mm2. Any way to see characteristics of medium voltage cable? Network is as on next pictures. MV side 13.5 kA, Trihal 1000 kVA, usc=6%. What are options in ecodial regarding MV cabling?

 

KrunoslavSever_0-1741018034688.jpeg

KrunoslavSever_1-1741018165236.jpeg

Any help is appriciated.

 

Best regards,

K

 

 

Labels
  • Labels:
  • Medium Voltage
  • Power Grid
  • Tags:
  • english
  • MV Cable
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Saravanakumar.L
Lieutenant Saravanakumar.L Lieutenant
Lieutenant

Posted: ‎2025-03-24 04:02 AM

1 Like
0
172
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-24 04:02 AM

 

Hello Krunoslavsever,

 

Thank you for sharing the cable specification.

 

Upon comparing the Ecodial data with the cable specification and short circuit data, we have determined that the short circuit values are considered for a duration of 1 second.

 

All values are aligned with a duration of 1 second, so it appears that Ecodial considers a 1-second withstand time, not 0.1 seconds.

 

This may clarify your query. 

 

Please feel free to ask any questions. 

 

Thanks & Regards,

Team- Ecodial Expert support. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Manon_Chaboud
Commander Manon_Chaboud Commander
Commander

Posted: ‎2025-03-10 01:07 AM

1 Like
0
329
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-10 01:07 AM

Hello @KrunoslavSever, thank you for your post, we'll come back to you!

Reply

Link copied. Please paste this link to share this article on your social media post.

Saravanakumar.L
Lieutenant Saravanakumar.L Lieutenant
Lieutenant

Posted: ‎2025-03-12 08:06 PM

1 Like
3
292
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-12 08:06 PM

Hello Krunoslavserver,

 

Thanks for reaching us!

 

Can you please provide the project file to analysis. 

 

Thanks & Regards,

Team - Ecodial expert support. 

Reply

Link copied. Please paste this link to share this article on your social media post.

KrunoslavSever
Ensign KrunoslavSever Ensign
Ensign

Posted: ‎2025-03-13 03:37 AM

In response to Saravanakumar.L
0 Likes
2
274
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-13 03:37 AM

Hi @Saravanakumar.L 

 

please find ecodial file attached.

 

BR,

K

Attachments
test file.EAC
Reply

Link copied. Please paste this link to share this article on your social media post.

Saravanakumar.L
Lieutenant Saravanakumar.L Lieutenant
Lieutenant

Posted: ‎2025-03-20 03:24 AM

In response to KrunoslavSever
0 Likes
1
218
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-20 03:24 AM

 

Hello Krunoslavsever,

 

I hope this message finds you well.

 

We have validated the query and found that the choice of MV cable depends on the IK3M specifications.

For instance, we modified the MV source short circuit current to 10.6kA, which resulted in the adoption of a      120 sqmm cable.

 

SaravanakumarL_0-1742466057801.png

SaravanakumarL_1-1742466085685.jpeg

 

 

 

As you know, Ecodial adheres to IEC standards, and all calculations are in line with these standards.

 

You mentioned that the manufacturer indicates a 70 sqmm cable is sufficient for short circuit values of 13.7kA. Could you please share the details regarding this cable?

 

Thanks & Regards, 

Team- Ecodial Expert support. 

Reply

Link copied. Please paste this link to share this article on your social media post.

KrunoslavSever
Ensign KrunoslavSever Ensign
Ensign

Posted: ‎2025-03-21 12:06 AM

In response to Saravanakumar.L
0 Likes
0
203
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-21 12:06 AM

Hello @Saravanakumar.L 

Thank you for your info. Details about the cables can be found in attachment. 

Best regards,

K

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Saravanakumar.L
Lieutenant Saravanakumar.L Lieutenant
Lieutenant

Posted: ‎2025-03-24 04:02 AM

1 Like
0
173
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-24 04:02 AM

 

Hello Krunoslavsever,

 

Thank you for sharing the cable specification.

 

Upon comparing the Ecodial data with the cable specification and short circuit data, we have determined that the short circuit values are considered for a duration of 1 second.

 

All values are aligned with a duration of 1 second, so it appears that Ecodial considers a 1-second withstand time, not 0.1 seconds.

 

This may clarify your query. 

 

Please feel free to ask any questions. 

 

Thanks & Regards,

Team- Ecodial Expert support. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of