Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-02-25 01:50 AM
Hi,
I received a question from a customer who is using Ecostruxure Power Design 5.3.1 INT:
Any comments? File is attached.
"Hello, why does changing the Number of trays and Touching circuits not change the cable calculation results?
Shouldn't it take into account the coefficients from table B 52-21?"
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-03-24 03:39 AM
Hello AnrejsRo,
We have validated the query and confirmed that the cable installation method of 32 F and the IEC standard IEC 60364-5-52 respective table indicate the following:
If we have a maximum of 9 cables, including the touching circuits, the correction factor is 0.78. This correction factor remains the same for up to 20 touching circuits, including the respective cables.
Therefore, the cable calculation maintains the same 0.78 correction factor as per the standard.
Hence, Ecodial is working as expected.
Thanks & Regards,
Team- Ecodial Expert support.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-02-27 12:36 AM
Hello @AndrejsRo, thank you for your post!
@Genghiz can you advise @AndrejsRo please?
Thank you in advance!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-03-12 08:09 PM
Hello AndrejsRo,
Thanks for reaching us!
We are working on your query.
Thanks & Regards,
Team- Ecodial expert support.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-03-24 03:39 AM
Hello AnrejsRo,
We have validated the query and confirmed that the cable installation method of 32 F and the IEC standard IEC 60364-5-52 respective table indicate the following:
If we have a maximum of 9 cables, including the touching circuits, the correction factor is 0.78. This correction factor remains the same for up to 20 touching circuits, including the respective cables.
Therefore, the cable calculation maintains the same 0.78 correction factor as per the standard.
Hence, Ecodial is working as expected.
Thanks & Regards,
Team- Ecodial Expert support.
Link copied. Please paste this link to share this article on your social media post.