Posted: 2024-11-29 03:25 AM
EcoStruxure Power Commission No Device Found Issue
I use EPC to connect and perform any action to a Circuit Breaker and Panel Server. I launched Device Discovery and detected a connection on one of the Com Ports (I am using USB/Serial). But when I tried to find the device, it showed "No Devices Found". I am using a Service Interface connected to a Micrologic.
EcoStruxture Power Commission Verson 2.33.0
- Labels:
-
Operations & Services
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-11-29 05:47 AM
Hello @dhtanap
We are not able to solve the issue through that platform
Please, contact your local CCC to open a technical case.
Don't forget to provide the log files from EPC software.
You could find and download the log files from the home page of EPC (see the picture below ) :
best regards
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-12-09 01:26 AM
I have already tried connecting my laptop, and it works fine now. Last week, I had the EPC uninstalled and installed again. To successfully uninstall, I downloaded EcoReachUninstaller and MicrosoftProgram_Install_Uninstall from the se.com website.
Now I can detect the com port and add a new device using the EPC.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-11-29 05:11 AM
Hello @dhtanap, thank you for your question!
@EPC_Leader, can you help @dhtanap regarding this issue?
Thank you in advance!
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-11-29 05:47 AM
Hello @dhtanap
We are not able to solve the issue through that platform
Please, contact your local CCC to open a technical case.
Don't forget to provide the log files from EPC software.
You could find and download the log files from the home page of EPC (see the picture below ) :
best regards
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-12-09 01:26 AM
I have already tried connecting my laptop, and it works fine now. Last week, I had the EPC uninstalled and installed again. To successfully uninstall, I downloaded EcoReachUninstaller and MicrosoftProgram_Install_Uninstall from the se.com website.
Now I can detect the com port and add a new device using the EPC.