EVLink Modbus Remote Start Restriction
  • Power Distribution IEC
  • EVLink Modbus Remote Start Restriction
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
80
J_Travostino
Sisko J_Travostino Sisko
70
EVlink Load Management System
NeiB
Lt. Commander NeiB Lt. Commander
Lt. Commander
Posted: ‎2023-02-22 05:52 AM . Last Modified: ‎2023-02-22 05:53 AM
1497
Hi All,
Please could you explain what does it mean that "Remote Start" is not possible as stated in the Modbus manual for EvLink, 7.5.1.5?
It is not quite clear to me if it refers to start the device as a reboot or is regarding starting the charge of the sockets which I believe is the address #150.
Thank you! Neide
  • Connectivity
Louis_LEVEQUE
Lieutenant JG Louis_LEVEQUE Lieutenant JG
Lieutenant JG
Posted: ‎2023-02-22 07:44 AM
1
1480
Hello Neide,
It is not possible to start a transaction (start a charge) through ModBus.
As soon as the transaction starts, you can suspend and restart through ModBus, but you can't start.
Is it clearer now ?
Best regards
Louis
Louis_LEVEQUE
Lieutenant JG
1
1481
Hello Neide,
Is it clearer now ?
Best regards
Louis
NeiB
Lt. Commander
Posted: ‎2023-02-22 10:35 AM
In response to Louis_LEVEQUE
Hi Louis, thank you very much for your prompt answer. Yes, now I understand better this point. So in a nutshell, once customer connects to the socket and all the conditions are met the charges begins and if he wants to stop and/or start via modbus, it is possible by address 150. Appreciate your help. Regards, Neide