Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-02-22 05:52 AM . Last Modified: 2023-02-22 05:53 AM
Hi All,
Please could you explain what does it mean that "Remote Start" is not possible as stated in the Modbus manual for EvLink, 7.5.1.5?
It is not quite clear to me if it refers to start the device as a reboot or is regarding starting the charge of the sockets which I believe is the address #150.
Thank you! Neide
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-02-22 07:44 AM
Hello Neide,
It is not possible to start a transaction (start a charge) through ModBus.
As soon as the transaction starts, you can suspend and restart through ModBus, but you can't start.
Is it clearer now ?
Best regards
Louis
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-02-22 07:44 AM
Hello Neide,
It is not possible to start a transaction (start a charge) through ModBus.
As soon as the transaction starts, you can suspend and restart through ModBus, but you can't start.
Is it clearer now ?
Best regards
Louis
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-02-22 10:35 AM
Hi Louis, thank you very much for your prompt answer. Yes, now I understand better this point. So in a nutshell, once customer connects to the socket and all the conditions are met the charges begins and if he wants to stop and/or start via modbus, it is possible by address 150. Appreciate your help. Regards, Neide
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.