EVLink Load Management System - Direct Serial Connection Communication Settings

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • EVLink Load Management System - Direct Serial Connection Communication Settings
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
80
J_Travostino
Sisko J_Travostino Sisko
70
View All

Recommended Forums

  • Comunidade de Soluções Elétricas

  • Expert on Demand for Standards & Regulations

Related Products
product field
Schneider Electric
EVlink Load Management System

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Start a Topic
Solved
swil
Commander swil
Commander

Posted: ‎2021-01-31 08:59 PM . Last Modified: ‎2022-02-02 01:51 AM

3 Likes
5
5287
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-01-31 08:59 PM . Last Modified: ‎2022-02-02 01:51 AM

EVLink Load Management System - Direct Serial Connection Communication Settings

Hi,

 

I can't seem to find an EVLInk forum. Is there one?

 

The HMIBSCEA53D1EDS LMS system installation guide and user guide do not seem to indicate what serial settings are appropriate for direct serial connection to a meter, or wiring connections.

 

I'm trying to connect an iEM3455 LVCT meter to the LMS.

 

Any assistance would be appreciated.

Labels
  • Labels:
  • Connectivity
  • eMobility
  • Sustainability
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
adrien-g
Ensign adrien-g Ensign
Ensign

Posted: ‎2021-02-01 09:10 AM

5 Likes
2
5244
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-02-01 09:10 AM

Dear @swil , 

 

Thank you for your question. You will find below some details on the way to connect a Power Meter to EVlink LMS using a Modbus Serial connection.

 

The picture below gives you information about plug and connectors to make the physical connection within your installation.

 

LMS RTUR cabling V0.jpg

 

You will find attach a datasheet of a sample 'USB to RS485' Serial Converter cable that we used to do such installation.

 

The picture below explains how to configure the Powermeter during the configuration. The RTU option has to be checked

EVlinkLMS_PM_Configuration.jpeg

 

I hope that these information will help you. Feel free to come back to us if you have additional question.

 

See Answer In Context

Attachments
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

adrien-g
Ensign adrien-g Ensign
Ensign

Posted: ‎2021-02-02 01:10 AM

In response to swil
1 Like
0
5225
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-02-02 01:10 AM

Dear swil,

 

Baud rate is '19200' and parity is 'none' which i guess are the default settings. COM.Protection has to be set to disable as well.

 

The serial connector should work as well for Direct Serial Connection with the Power Meter.

 

Adrien

 

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
J_Travostino
Sisko J_Travostino Sisko
Sisko

Posted: ‎2021-02-01 05:09 AM

2 Likes
0
5251
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-02-01 05:09 AM

Hello @swil 

 

Thanks for reaching us.

As we currently do not have a dedicated forum on EVLink, you are at the right place.

 

We'll be back to you pretty soon.

 

BR

 

Julien Travostino
Power Distribution & Digital forum community owner
Power Products Div.
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

adrien-g
Ensign adrien-g Ensign
Ensign

Posted: ‎2021-02-01 09:10 AM

5 Likes
2
5245
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-02-01 09:10 AM

Dear @swil , 

 

Thank you for your question. You will find below some details on the way to connect a Power Meter to EVlink LMS using a Modbus Serial connection.

 

The picture below gives you information about plug and connectors to make the physical connection within your installation.

 

LMS RTUR cabling V0.jpg

 

You will find attach a datasheet of a sample 'USB to RS485' Serial Converter cable that we used to do such installation.

 

The picture below explains how to configure the Powermeter during the configuration. The RTU option has to be checked

EVlinkLMS_PM_Configuration.jpeg

 

I hope that these information will help you. Feel free to come back to us if you have additional question.

 

Attachments
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

swil
Commander swil
Commander

Posted: ‎2021-02-01 02:29 PM

In response to adrien-g
1 Like
1
5237
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-02-01 02:29 PM

Thank you, @adrien-g. I will try to locate that USB hardware.  The only hint as to how to connect LMS directly to serial meters in the user manual/installation is shown in the attached image.

 

I have two additional questions:

1. Have you used this method to connect a iEM3x5x meter directly over serial to an LMS unit? 

2. Were the baud rate / parity settings used the factory default settings for the iEM3x5x meter?

 

 

Attachments
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

adrien-g
Ensign adrien-g Ensign
Ensign

Posted: ‎2021-02-02 01:10 AM

In response to swil
1 Like
0
5226
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-02-02 01:10 AM

Dear swil,

 

Baud rate is '19200' and parity is 'none' which i guess are the default settings. COM.Protection has to be set to disable as well.

 

The serial connector should work as well for Direct Serial Connection with the Power Meter.

 

Adrien

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

SebTTG
Lieutenant SebTTG Lieutenant
Lieutenant

Posted: ‎2021-02-24 01:27 AM

0 Likes
0
5080
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-02-24 01:27 AM

Great sharing ! Thanks

STT - EcoXpert LV & MV badge owner
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.