Cable Thermal Stress Curves
Hi,
How do you show the cable curves on the protection curve tab?
- Labels:
-
Power Distribution Software
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-12-07 03:44 AM
Hello,
Thanks for reaching the “EcoStruxure Power Design Forum.”
In Ecodial application, the cable curve can be seen along with the protection on the ‘Curves’ tab.
Steps:
- Ensure the network calculation is completed.
- Select the circuit at which the ‘cable curve’ needs to be analyzed.
- Click on the ‘Protection’ (circuit breaker), the same is highlighted in green now.
- Click on the ‘Curves’ tab.
- Select from the drop down, the choice as ‘Cable.’
Cable Curve
Conclusion:
Through the above steps, you will be able to see the ‘required cable curves’ along with the protection available for that circuit.
Thanks & Regards,
Team - Ecodial Expert Support.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-12-07 03:44 AM
Hello,
Thanks for reaching the “EcoStruxure Power Design Forum.”
In Ecodial application, the cable curve can be seen along with the protection on the ‘Curves’ tab.
Steps:
- Ensure the network calculation is completed.
- Select the circuit at which the ‘cable curve’ needs to be analyzed.
- Click on the ‘Protection’ (circuit breaker), the same is highlighted in green now.
- Click on the ‘Curves’ tab.
- Select from the drop down, the choice as ‘Cable.’
Cable Curve
Conclusion:
Through the above steps, you will be able to see the ‘required cable curves’ along with the protection available for that circuit.
Thanks & Regards,
Team - Ecodial Expert Support.