Application download via FTP – keep an eye on the transfer type!
When transferring text files to the controller, consider switching your FTP client into binary transfer type to avoid conversions of Carriage Return + LineFeed character pairs into single LineFeed.
If you do not follow the recommendation, variable values may not be shown in the visualization / webvisualization.