New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
prog modicon
Modicon PAC Forum
A forum for topics related to the scope of Modicon PAC offers and ecosystem along the whole lifecycle: Modicon M580 and 340, EcoStruxure Control Expert, EcoStruxure Process Expert (Unity Pro) and more.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-2703:08 AM
prog modicon
Bonjour, je dois programmer plusieurs modicon avec principalement des entrées numériques que je dois ensuite aller lire sur un as-p pour une supervision. J'ai crée des lignes de prog pour chaque entrée avec en bout une bobine avec un %M0 %M1 etc mais sur l'asp je n'arrive pas à le lire.
J'ai bien créé le modbus tcp device ensuite j'ai essayé point par point ou alors des points d'entrée multi-bit sans succès je ne vois jamais cette valeur changer.
Du coup sur le modicon ai-je bien programmer ?
ps : J'ai bien trouver mon modicon sur la workstation
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-2709:38 PM
Good day Anthony,
Yes your programme is correct, however the data type for the %M would be Output Bits in the SCADA. I would rather recommend using holding Register bits. You can choose a %MW and map all the bits to it in the format %MW101:X0-X15 like in this example