I'm trying to write my HMI server time to the RRTC on a M580. I have been referencing the technote:
"In the M580 CPU, why does the system word %SW51 (RTC Hour) show a different value?"
I'm reading from the RRTC just fine using this note. I can also write to the system variables (%SWXX), but not the hour. Is there an elegant way to write to the RRTC that doesn't use the defunct system word %SW51 (RTC Hour)?
Thanks,
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-02-01 08:51 PM
I am not sure why you are having the issue. Please note that the RTC is organized as per the attached document. %SW51 is expressed in hex and contains 16#HHMM where HH is the hexadecimal equivalent of hours 0-23 and MM is 0-59 minutes.
see the system word manual.. https://www.se.com/au/en/download/document/EIO0000002135
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-02-04 04:45 PM
The M580 uses UTC in one and local time in the other. I can't remember which way around. That will account for your different values. We had to modify our PLC clock RTC sync DFB to accommodate this difference from the M340.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-02-05 05:40 AM
RRTC block has only outputs so you will not be able to write to it.
I believe you should be able to use local time with WRTC_DT block.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-05-02 01:44 AM
I am not sure why you are having the issue. Please note that the RTC is organized as per the attached document. %SW51 is expressed in hex and contains 16#HHMM where HH is the hexadecimal equivalent of hours 0-23 and MM is 0-59 minutes.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.