Voltage related information for BMXSDO0802

Modicon PAC Forum

A forum for topics related to the scope of Modicon PAC offers and ecosystem along the whole lifecycle: Modicon M580 and 340, EcoStruxure Control Expert, EcoStruxure Process Expert (Unity Pro) and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Modicon PAC Forum
  • Voltage related information for BMXSDO0802
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Trinxs1
Lt. Commander Trinxs1 Lt. Commander
10
YONGHO-KIM
Lieutenant YONGHO-KIM Lieutenant
9
ciupol
Lieutenant ciupol
9
RoozeeR
Lt. Commander RoozeeR Lt. Commander
8
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Modicon PAC Forum
Solved
YONGHO-KIM
Lieutenant YONGHO-KIM Lieutenant
Lieutenant

Posted: ‎2025-08-17 11:26 PM

0 Likes
1
43
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-08-17 11:26 PM

Voltage related information for BMXSDO0802

 

1. The configuration settings for BMXSDO802 are as follows.

Image.png

 

2. The cable between the field device and the PLC panel is currently not connected.

 

3. Voltage is being measured at the terminal block and the output module in the PLC to check the health of each channel.

 

4. When each channel of the BMXSDO0802 is controlled and measured using a Multi-meter, the following voltages are observed: 

  - 0 (False): 18 - 19VDC

  - 1 (True): 23 - 24VDC

 

5. The question is: when the output is set to 0(False), the Multi-meter still reads approximately 18.5VDC. Why is voltage present even when the output is turned off?

 

 

Labels
  • Labels:
  • 03. Modicon PAC Safety
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Next Topic

Accepted Solutions
YONGHO-KIM
Lieutenant YONGHO-KIM Lieutenant
Lieutenant

Posted: ‎2025-08-20 12:05 AM

0 Likes
0
29
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-08-20 12:05 AM

Importantly, this 19v reding does not indicate a fault of risk of unintended activation. The BMXSDO0802 module complies with IEC 61131-2 standards, which specify that a de-energized output must not supply more than 0.5mA of current. The module adheres to this requirement, ensuring that the leakage current remains below this threshold. As a result, the output remains in a true de-energized state and cannot activate any connected actuator.

 

1) Characteristics of Solid-State Output

  • Solid-state outputs typically use transistors to control ON/OFF states.
  • Even when the output is OFF, a small leakage current (up to 0.5mA) may flow due to the nature of transistors.
  • As a result, the circuit may not appear to be completely open in a physical sense.

2) Residual Voltage When Load Is Not Connected

  • If no load is connected to the output terminal, the terminal may become floating, and the potential difference in the internal circuit can be detected by a multimeter.
  • This can result in a residual voltage being measured (e.g., approximately 18V).
  • On the other hand, when a load is connected, the leakage current flows to ground through the load, and the output terminal voltage drops to nearly 0V.
  • In other words, the output is not actually ON, and this is a normal behavior based on circuit characteristics.

3) High Impedance Characteristics of Digital Multimeters

  • Digital multimeters generally have a high input impedance (typically over 10MΩ), allowing measurements with minimal impact on the circuit.
  • Due to this high impedance, residual voltage can be sensitively detected.
  • Therefore, measuring around 18V at the output terminal in the OFF state is a normal phenomenon caused by both the circuit and multimeter characteristics."

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
YONGHO-KIM
Lieutenant YONGHO-KIM Lieutenant
Lieutenant

Posted: ‎2025-08-20 12:05 AM

0 Likes
0
30
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-08-20 12:05 AM

Importantly, this 19v reding does not indicate a fault of risk of unintended activation. The BMXSDO0802 module complies with IEC 61131-2 standards, which specify that a de-energized output must not supply more than 0.5mA of current. The module adheres to this requirement, ensuring that the leakage current remains below this threshold. As a result, the output remains in a true de-energized state and cannot activate any connected actuator.

 

1) Characteristics of Solid-State Output

  • Solid-state outputs typically use transistors to control ON/OFF states.
  • Even when the output is OFF, a small leakage current (up to 0.5mA) may flow due to the nature of transistors.
  • As a result, the circuit may not appear to be completely open in a physical sense.

2) Residual Voltage When Load Is Not Connected

  • If no load is connected to the output terminal, the terminal may become floating, and the potential difference in the internal circuit can be detected by a multimeter.
  • This can result in a residual voltage being measured (e.g., approximately 18V).
  • On the other hand, when a load is connected, the leakage current flows to ground through the load, and the output terminal voltage drops to nearly 0V.
  • In other words, the output is not actually ON, and this is a normal behavior based on circuit characteristics.

3) High Impedance Characteristics of Digital Multimeters

  • Digital multimeters generally have a high input impedance (typically over 10MΩ), allowing measurements with minimal impact on the circuit.
  • Due to this high impedance, residual voltage can be sensitively detected.
  • Therefore, measuring around 18V at the output terminal in the OFF state is a normal phenomenon caused by both the circuit and multimeter characteristics."

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of