1. The configuration settings for BMXSDO802 are as follows.
2. The cable between the field device and the PLC panel is currently not connected.
3. Voltage is being measured at the terminal block and the output module in the PLC to check the health of each channel.
4. When each channel of the BMXSDO0802 is controlled and measured using a Multi-meter, the following voltages are observed:
- 0 (False): 18 - 19VDC
- 1 (True): 23 - 24VDC
5. The question is: when the output is set to 0(False), the Multi-meter still reads approximately 18.5VDC. Why is voltage present even when the output is turned off?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-08-20 12:05 AM
Importantly, this 19v reding does not indicate a fault of risk of unintended activation. The BMXSDO0802 module complies with IEC 61131-2 standards, which specify that a de-energized output must not supply more than 0.5mA of current. The module adheres to this requirement, ensuring that the leakage current remains below this threshold. As a result, the output remains in a true de-energized state and cannot activate any connected actuator.
1) Characteristics of Solid-State Output
2) Residual Voltage When Load Is Not Connected
3) High Impedance Characteristics of Digital Multimeters
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-08-20 12:05 AM
Importantly, this 19v reding does not indicate a fault of risk of unintended activation. The BMXSDO0802 module complies with IEC 61131-2 standards, which specify that a de-energized output must not supply more than 0.5mA of current. The module adheres to this requirement, ensuring that the leakage current remains below this threshold. As a result, the output remains in a true de-energized state and cannot activate any connected actuator.
1) Characteristics of Solid-State Output
2) Residual Voltage When Load Is Not Connected
3) High Impedance Characteristics of Digital Multimeters