M580 BMEH584040 AS STANDALONE

Modicon PAC Forum

A forum for topics related to the scope of Modicon PAC offers and ecosystem along the whole lifecycle: Modicon M580 and 340, EcoStruxure Control Expert, EcoStruxure Process Expert (Unity Pro) and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Modicon PAC Forum
  • M580 BMEH584040 AS STANDALONE
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Trinxs1
Lt. Commander Trinxs1 Lt. Commander
11
YONGHO-KIM
Lieutenant YONGHO-KIM Lieutenant
9
ciupol
Lieutenant ciupol
9
RoozeeR
Lt. Commander RoozeeR Lt. Commander
8
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Modicon PAC Forum
Start a Topic
Alfo1987
Crewman Alfo1987
Crewman

Posted: ‎2025-08-14 06:59 AM

0 Likes
4
208
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-08-14 06:59 AM

M580 BMEH584040 AS STANDALONE

Hello, I hope you have a nice day.

My intention is to start a scalable M580 system, starting with a BMEH584040 CPU operating as a standalone unit, and then in the future add a new main rack with a second BMEH584040, operating redundantly. Do you think this is possible? That the BMEH584040 CPU can be configured and operate independently, without triggering fault alarms. Or do I necessarily need to use a standalone CPU and install two new redundant CPUs in the future?

 

VERY THANKS!

Labels
  • Labels:
  • 02. Modicon M580 ePAC
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
Trinxs1
Lt. Commander Trinxs1 Lt. Commander
Lt. Commander

Posted: ‎2025-08-26 07:42 PM

1 Like
1
162
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-08-26 07:42 PM

Alfo1987 this is not standard practice, but it is possible for you to do this.  In reality if a CPU fails the other must operate in stand-alone mode.  Be aware that you cannot install any IO in the CPU rack.  Depending on the IO selected you may have to:

  • Install a second rack, power supply, CRA module and X80 IO or
  • Use distributed IO such as Edge IO NTS or STB advantys, Intelligent Ethernet Device (drive) with a BMENOS0300 or Ethernet module to connect to this IO device.
Trinxs
Senior Technical Sales Consultant - PAC
Reply

Link copied. Please paste this link to share this article on your social media post.

Rico94
Crewman Rico94 Crewman
Crewman

Posted: ‎2025-08-26 11:49 PM

1 Like
1
141
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-08-26 11:49 PM

Hello, in the configuration of the Hsby CPU you can deactivate the state online of one of the CPU

Reply

Link copied. Please paste this link to share this article on your social media post.

Alfo1987
Crewman Alfo1987
Crewman

Posted: ‎2025-08-28 05:42 AM

In response to Trinxs1
0 Likes
0
99
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-08-28 05:42 AM

Hello Trinxs1, thank you very much! Of course, everything will be designed to operate with a Hot Standby system with BMXCRA31210 on both I/O racks. In the future, we'll add more I/O racks, including the second CPU rack, to complete the redundant system and run more critical functions on it.

Reply

Link copied. Please paste this link to share this article on your social media post.

Alfo1987
Crewman Alfo1987
Crewman

Posted: ‎2025-08-28 05:43 AM

In response to Rico94
0 Likes
0
99
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-08-28 05:43 AM

Rico94, very thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore