Quantum S908 HSBY to M580H migration via QSA 140CRA31908 adapter
Modicon PAC Forum
A forum for topics related to the scope of Modicon PAC offers and ecosystem along the whole lifecycle: Modicon M580 and 340, EcoStruxure Control Expert, EcoStruxure Process Expert (Unity Pro) and more.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-05-0905:28 PM. Last Modified: 2024-05-0905:34 PM
Quantum S908 HSBY to M580H migration via QSA 140CRA31908 adapter
Hi, I am preparing to perform a Quantum S908 HSBY system to a M580H migration, keeping the old S908 drops and using de 140CRA31908 adapters. I have the following questions:
1. Because the migration was originally from Concept to Control Expert, and then processed via UMAC, some things regarding the toplogy couldn't be mapped right. For instance, the original Concept CPU used a CHS redundancy card, and after the Concept to Control Expert conversion, the resulting Control Expert File included a Unity Quantum redundant CPU, instead of the original CPU and CHS. Then, after the UMAC conversion, it shows a non-redundant P584040 with just one 140CRA31908 drop.
2. Because I'm using dual 140CRA31908 adapters (replacing the Quantum CPUs), what should be the positions of the rotary switches of both adapters? should they be different? after all, this are now treated as X80 drops of the M580 system.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-05-1607:03 AM
My recommendation is to convert from Concept to Control Expert first keeping the Quantum Processors and IO and resolve all errors first. I think you have to change the processor yourself to a Quantum HSBY processor as the CHS module is not supported, if I recall the conversion tries to keep your original processor do a change processor and select one of the 140 CPU 67X XX processors. When you use UMAC, I believe there's a configuration setting for the processor, if not you should be able to change the processor after the conversion.
To answer your second question, one CRA will be set to drop 1 and the other set to drop 2. In control expert you'll treat both as regular EIO drops.