Posted: 2025-03-05 02:23 AM
Hi All,
The ABE7 Telefast system, only provides pre-wired cables to I/O cards that have HE10 connectors, Sub-D connectors, 40-way connectors or legacy Controller Platforms. It doesn't appear to provide pre-wired cables for lower density X80 I/O with BMXFTB2xxx terminal blocks. So it seems I have to make one. The options appear to be:
I'm leaning towards Option 2. Has anyone done this and does ? And more's the point, does anyone have a diagram showing the TWDFCWxxx pinouts / wire colors ?
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-03-05 05:07 AM
There are cables available for 20 and 28-way X80 connectors. For 20-way it is BMXfta1522 and BMXFTA3022. For 28-way connector it is BMXFTA150 and BMXFTA300. If you want to know which ABE7 bases are compatible with which X80 module go to module website on Schneider website and click Options.

Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-07-02 06:07 AM
Hi Ciupol,
Thanks for the reply.
Unfortunately the cables that you reference are purely for HART/analogue and analogue I/O modules to ABE7 Telefast.
I was looking for pre-wired cables for the 16 channel discrete I/O modules that use the BMXFTB20x0 Field Terminal Blocks, i.e. Cables with BMXFTB20x0 on one end and HE10 Connectors on the other for connection to an ABE7 Telefast Sub-base. They don't exist from Schneider Electric.