Hi everyone. We are quite new in M580S and still learning.
We are working on a project using M580S with CRA31210 module configured for a remote drop. Kindly refer attached architecture.
After setting up all equipment, powered up and downloaded the configuration, we noticed that all I/O modules are having: -
Besides that, the CRA module is having LED RUN (green) - off as well.
Kindly clarify, is the error on I/O modules are related to the CRA? Kindly guide us on how to troubleshoot this problem. Thank you very much.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-06-30 08:05 PM
Hi all. Just to update the status.
We finally confirmed the I/O modules LED ERR (red) - blinking was due to BMECRA31210 firmware ver. 2.40 incompatibility with CPU firmware ver. 3.20.05. It requires a firmware 2.60 or later.
We downloaded SV2.60 and upgraded BMECRA31210 firmware accordingly. After some adjustments, we managed to solve the issue. Thanks again.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-06-26 10:13 PM
Check and correct CRA drop address switches
> The CRA31210 uses rotary switches to set its drop address.
> If the address is not correctly set or doesn't match the configuration in Control Expert, the I/O Modules will not be recognized.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-06-27 03:43 AM
Hi @YONGHO-KIM ,
Thank you for your response. We have set CRA drop address switches as below: -
We further checked the CRA firmware ver. is 2.4. Could it be due to incompatibility issue with CPU firmware ver. 3.2? If yes, is there a way to upgrade the CRA firmware? Thank you.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-06-30 08:05 PM
Hi all. Just to update the status.
We finally confirmed the I/O modules LED ERR (red) - blinking was due to BMECRA31210 firmware ver. 2.40 incompatibility with CPU firmware ver. 3.20.05. It requires a firmware 2.60 or later.
We downloaded SV2.60 and upgraded BMECRA31210 firmware accordingly. After some adjustments, we managed to solve the issue. Thanks again.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-07-01 12:32 AM
Hello Eyanto,
You have downloaded a configuration, which include the CRA31210 and the IO modules?
At least the CRA must have a RUN light on. Please check for the CRA module:
1: Is the switch on front of the module set o the configured Drop address?
2: Is the configured module selected correctly: Is it according the module type BMXCRA31210 or BMECRA31210? This is a common mistake, if the type is not set correct as it's only 1 letter difference (X or E).
br
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-07-01 02:08 AM
Hi @RoozeeR ,
Yes, we have downloaded the configuration with BMECRA31210 and X80 I/O modules. The CRA rotary address switches have been set as below: -
Now the CRA indicates LED RUN (green). Thank you.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of